I have an Ideal Vogue C40 Gen 2 40kw combi boiler hooked up to a 10 radiator CH system. Recently I have balanced the rads and now have a feed temp of 60 and return temp of around 40 degrees. I’m not sure the boiler is condensing. There’s plumes of vapour coming out the flue and the onboard efficiency monitor seems to always be at 40%. Any suggestions?
 
Return is well below 50 yes it’s condensing ignore the efficiency bar
 
Have a read of this it explains it better than me
 

Attachments

  • Screenshot_20221106-141416.png
    Screenshot_20221106-141416.png
    154.9 KB · Views: 8
  • Screenshot_20221106-141933.png
    Screenshot_20221106-141933.png
    138.1 KB · Views: 9
  • Screenshot_20221106-141952.png
    Screenshot_20221106-141952.png
    144 KB · Views: 9

Reply to Is my boiler condensing? in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

C
I’ve had an Ideal Vogue 32max/gen2 system boiler to a Megaflo fitted a week and running it at Flow temp 73 degrees to getting a return temp of about 55 degrees C, I’m seeing the LCD screen saying the efficiency level is only 25-28%. Has anyone else seen such a low percentage? I know for a fact...
Replies
2
Views
362
Hi, I have an 20yrs heat only potterton 50e boiler with 196x old house - suspended floor - designer radiators, open vent system and hot water cylinder on first floor with two motorised valves and stat. I want to replace the boiler with minimal cost and max efficiency so thinking of replacing...
Replies
1
Views
600
Hello friends - I really struggle to understand my heating and hot water system I posted my question on Diynot but it ended up being five pages and couldnt get to the bottom of it and I thought worth asking the elders on here for their view - Hot water temp is 40 Degrees - Ideal Mexico 2...
Replies
10
Views
717
R
Wb 4000 recently installed, and just balanced the rads with around 16 degree delta across most rads. I'm trying to make sure that the return temperature to the boiler are less than 55 degrees to ensure condensing is occurring. But in the service menu it only shows the primary heat exchanger...
Replies
0
Views
367
Return temperature
R
WB 4000 installed a few months back, just balanced the 7 rads - managed to get around 15 degrees delta across most rads. Not quite the 20 degrees but still. Flow set to 60 degrees for now. 1.Obviously I want to ensure the return temperature into the boiler is below the 55 ish degrees needed for...
Replies
2
Views
604
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock