Hi I have changed my Honeywell T6360 thermostat to a Salus T105RF wireless thermostat.
There was three wires going to the original honeywell thermostat. One of these being the supply and another going to the boiler. I wasn't sure what the other wire was and so didn't connect up.
Now the Salus thermostat has been working fine, but when the thermostat is not calling for heat and there is demand for hot water (unvented hot water cylinder) the radiators are still getting warm.
Am I right in thinking that the other wire is for the heating 2 port valve?
If so, what terminal do I connect the valve wire too in the Salus reciever unit as there are only two terminals (NO & COM)?
Do I just connect the valve wire to the same terminal as the wire to the boiler?
Thanks for any advice/help
David
 

Attachments

    You don't have permission to view attachments. Attachments are hidden.

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
Messages
33,452
Solutions
3
Sunvic port valve ?
 

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
Messages
33,452
Solutions
3
Why does it have a wire in port 4 then eg heating off ?
 

DavidB

Messages
11
I have three 2port valves, two for both hot water cylinders and one for the heating.
I'm assuming when the programer is calling for hot water and the heating thermostat is not calling for heat the valve is not closing. I think maybe the wire is for this valve hence it not closing under the above conditions?
 

ChrisB1982

Plumber
Gas Engineer
Messages
2,727
Solutions
2
Sounds more like the heating zone valve isn’t shutting off. How come you have x2 cylinders?
 

Reply to Honeywell T6360 Thermostat in the Central Heating Forum area at PlumbersForums.net

Similar threads

P
  • Question
You'd find the thermostat wires (prob in airing cbd) and terminate/link out red and yellow. Either fit relay inplace of existing timer or...
Replies
1
Views
492
Knappers
K
H
Want to replace an old thermostat (heat only) with a Sensi Smart thermo. Same needs a C wire. Can I connect the C wire to to the pos terminal on...
Replies
0
Views
184
Hawksnestl
H
johnch121
I’m guessing red live that goes to com Yellow switch that goes to w Make safe the blue eg choc block
Replies
1
Views
372
ShaunCorbs
ShaunCorbs
Beshman
  • Question
Well, I don't really know. I was thinking the Logic Halo or one of the wifi Tado products. But I'd rather have something I can just plug in and use
Replies
4
Views
365
Beshman
Beshman
R
Either will be fine also your salus will fit volt free means the relay isn’t Powered eg low voltage but mains voltage is ok for it as well
Replies
4
Views
618
ShaunCorbs
ShaunCorbs
Creating content since 2001. Untold Media is a Registered Trademark.

Newest Threads (Please Reply)

Search Forum

Top