Ive been back and it was the nozzle. Adjusted air and got the right settings. Ill never trust a new nozzle again!
 
Ive been back and it was the nozzle. Adjusted air and got the right settings. Ill never trust a new nozzle again!

I thought it was nozzle. That's good to hear back what it was. If the nozzle was handled, or a tiny bit of dirt or water inside it could do that.
You would assume the burners are final test fired, but probably not fully tested.
I have had new nozzles I installed on services being totally faulty, but only rarely and never on new boilers/burners.
 
quick check if you come across this again, pull off the air intake hose and put a bit of card part way across the inlet, move this further over to restrict the air intake to simulate a choke flap
 
quick check if you come across this again, pull off the air intake hose and put a bit of card part way across the inlet, move this further over to restrict the air intake to simulate a choke flap

Thick wall 28mm pipe insulation is a perfect fit in the snorkel.
This has got me out of trouble after finding no secondary air damper disc when altering
boiler output.Works a treats on the RDB.
Anybody got a source for the air damper discs?Not easy to come by.
 
I have had this a few times recently where the wrong nozzle is in the wrong box eg. 0.7580EH on the box and the actual nozzle is 0.6580EH for instance. This has only recently started to happen and we have known it on at least 4 nozzles in the last 6 months
 
I have had this a few times recently where the wrong nozzle is in the wrong box eg. 0.7580EH on the box and the actual nozzle is 0.6580EH for instance. This has only recently started to happen and we have known it on at least 4 nozzles in the last 6 months

I check each nozzle is correct size just as I am about to fit it, for that reason.
But if I were you I wouldn't be happy to continue buying them from your supplier of they are allowing nozzle containers to be opened. They really shouldn't be handled
 
I have had this a few times recently where the wrong nozzle is in the wrong box eg. 0.7580EH on the box and the actual nozzle is 0.6580EH for instance. This has only recently started to happen and we have known it on at least 4 nozzles in the last 6 months

I check each nozzle is correct size just as I am about to fit it, for that reason.
But if I were you I wouldn't be happy to continue buying them from your supplier of they are allowing nozzle containers to be opened. They really shouldn't be handled
 
Status
Not open for further replies.

Reply to Grant air adjustment in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Grant Vortex 50/90 condensing oil boiler where the air tube spigot over the fan is not connected to the existing flue, should this be closed off...
Replies
1
Views
377
I have a Grant Vortex Blue 26kw external oil boiler, installed less than 12 months ago. It's had intermittent non-starting problems resulting in...
Replies
5
Views
874
About 12 days ago attended a boiler lock out. Apparently another plumber was there a week before to and adjusted the photo cell. .. It is a grant...
Replies
25
Views
3K
Hi, Newbie here so feel free to teach me the etiquette of this place, and apologies for the lengthy opening post. The boiler started locking out...
Replies
4
Views
736
J
I have a new Grant Vortex 15/26 oil boiler installed. It has a boiler thermostat with no numerical information, just a wedge graphic and covers...
Replies
8
Views
7K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock