I have an older Geberit, installed in 2009 (see photo). All the videos that I can find are about much newer models. No matter where I set the fill level, it over fills and pours down the overflow into the bowl, causing the filling to continue forever. The filling mechanism is quite recent, but clearly has a problem. Does anyone have this model, and how should I proceed? Thanks.
 

Attachments

  • F63A0702-01AD-4855-8CB8-7ADABAAB09B6.jpeg
    F63A0702-01AD-4855-8CB8-7ADABAAB09B6.jpeg
    238.1 KB · Views: 8
If it’s new, it is unlikely to need a new diaphragm. More likely is that there is some grit in the valve that is stopping it shutting off. Remove the valve, dismantle/clean/reassemble - before refitting it run some water into the cistern to clear the supply pipe.
 
Thank you. I’ve taken it out and cleaned it and restored it and it’s working so far. But, it had been working intermittently. Just in case, I’ve ordered a replacement part. I replaced it a few years ago (3 or 4) but had already forgotten how to take it apart. This time, I’ve made notes. The part is branded SIAMP.
 

Reply to Geberit enclosed cistern in the DIY Plumbing Forum area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
230
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
365
Hi they used to say as a last resort you could discharge the D2 pipework at high level and turn it back to the wall. Similar to a combi boiler. I have just looked back through the regs this seems to have changed and it isn't mentioned now. It now mentions if at high level it should be discharged...
Replies
11
Views
287
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
311
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
284
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock