D

Doodlebug

British Gas engineers are being advised not to use gas rate apps as tests have shown them to be inaccurate and unreliable.
 
When i had my gassafe inspection not long since, he asked me why when i had an i-phone i wasn't using an app. for this. I replied that i had it but thought he would want to see me work it out to which he replied , use the app !!!
 
This is fresh news briefed today, British Gas have instructed the whole workforce not to use any gas rate apps, we have had to sign to say we have had the brief.
 
I had same brief a month or so ago.
I have compared the apps, to BG's computer and also manual calcs and there is a difference between all, but nothing more than 5% or so.
 
but it's just a stopwatch and a calculator in one how can they possibly get it wrong, and if they did it would be wrong every time rather than here or there.

Gas rating is hardly an exact science anyway especially with these new card meters that you have to push buttons and wait etc, as long as you are in the ball park area your fine! 5% above and 10% below isn't it?
 
Last edited:
All I know is we have been told they are immaculate and can't be relied on.
 
I believe it is BG just trying to standardise the process for itself by making sure all its engineers use the laptop.
The G/R calculation process by any means is not an exact science.
 
hi all ,new to these forums, anyone know if theres an app for blackberry? can't seem to find it if there is, thanks
 
People still use those blackberrys?
I know what I would be asking santa for.:tongue3:
 
It's just a mathematic equation it can't be wrong. There is more chance of human error recording the figures or timing it wrong!
 
Well when it goes Pete Tong, you can say you heard it here first. ;-)
 
mine works good enough for me. Probably a BG engineer failed internal audit and blamed his iphone LOL.
 
Or B.G not liking the fact that something without a Britsh Gas logo and overinflated price tag is being used on one of their jobs.
 
when the bg app comes out it will abort the test halfway and demand the system is powerflushed and a co detector fitted before you get the answer
 
To be fair to them you can't blame them if they don't want their blokes to use it. The laptop has a programme to do it for you. So if they want all their blokes to use that then everyone's gas rate will be as per their own programme and everything confirms to what they want.

If their has been known discrepancies on the iPhone app then you can't blame anyone fr not wanting to use it, especially a firm the size of BG. If they made a mistake using this app then coud you imagine the uproar, so they've banned it and their till getting stick. They can't win either way really.

I personally don't this app I use a calculator. I was toying with paying for the app but this post would be enough for me not to bother.
 
Last edited:
The calculations will vary region to region according to the calorific value of the gas. Unless you know and use that in your calcs you are working to an approximation.
 
The calculations will vary region to region according to the calorific value of the gas. Unless you know and use that in your calcs you are working to an approximation.

I was thinking same, how many check bills for correct CV?
 
No mention of checking the cv of the gas in any text book or reg I have seen. The difference is probably that minimal it has no affect.
 
Sutely the badged input rating of the boiler would have to make an assumption on the CV of the fuel as well though, so in effect it doesn't matter. Only gas rating to determine the correct quantity of fuel is being used by the appliance, not to actually calculated heat production.
 
Well if BG say so then I'm ditching mine :willy_nilly:

Be better teaching some of the lads the back boilers need ventilation!
 
Well if BG say so then I'm ditching mine :willy_nilly:

Be better teaching some of the lads the back boilers need ventilation!

Are you suggesting British Gas engineers work unsafely?


Sent from my iPad using Tapatalk HD
 
Are you suggesting British Gas engineers work unsafely?


Sent from my iPad using Tapatalk HD
I'm saying I regularly go to CF installs with no ventilation that used to be under a BG contract since installation but they can't afford it, when I tell them what needs doing I normally get asked to leave because "British Gas never mentioned that".

I can only speak from e pertinence and I wish I had a pound for every time it's happened.
 
I'm saying I regularly go to CF installs with no ventilation that used to be under a BG contract since installation but they can't afford it, when I tell them what needs doing I normally get asked to leave because "British Gas never mentioned that".

I can only speak from e pertinence and I wish I had a pound for every time it's happened.

Ive never been to a job anywhere for anyone where an open flued boiler has had no vents, blocked up vents yes, but no vent at all, no.
I for one know that safety is drummed into engineers at BG and there lads wouldn't miss this and if they did then it would be a massive defect and heads would roll.
 
The calorific value can make quite a difference to the calculations.
The cv of gas supplied through the grid varies from between 37.5 - 43MJ/mÂł and the quoted values vary constantly.
No matter how you choose to work it out there has to be a margin for tolerance as you will never have the exact figures.

The calculation is MW Ă· cv = mÂł/s or simplified to the units we use (kW and mÂł/hr) we use kW x 3.6 Ă· cv = mÂł/hr
To do it from mÂł/hr - kW the formula is mÂł/hr x cv Ă· 3.6 = kW

As an example, say on a boiler burning 3scm/hr
If the calorific value of the gas was 37.5 the HI would be

3 x 37.5 Ă· 3.6 = 31.25kW

same boiler burning 3scm/hr at 40.5 MJ/mÂł

3 x 40.5 Ă· 3.6 = 33.75kW

same again at a cv of 43MJ/mÂł

3 x 43 Ă· 3.6 = 35.83kW

A bit of a difference.

BG wanting to ban the use of apps is not because they are wrong. They are not. They will just want to standardise their info they receive back by having there guys use the same method.
 
BG wanting to ban the use of apps is not because they are wrong. They are not. They will just want to standardise their info they receive back by having there guys use the same method.
Exactly! As I touched on previously. :wink_smile:
 
British Gas aren't likely to approve the use of a gas rate app which has passed no industry tests now are they. ;-)


Sent from my iPad using Tapatalk HD
 
The point i'm trying to make is the badged heat input on the appliance will have been based on a calorific value used at the time of the test. So even if you can find out the C.V of the gas, you can't compared egg's with egg's.

By gas rating the appliance you are only confirming that the appliance is using the right amount of fuel in the given time. Because the gas consumption information is rarely available on site, the industry seem to have decided to adopt the technique of converting f3/hr or m3/hr into KW in an attempt to simplify the process. The reality is it makes for a pretty crude and inaccurate calculation for heat input but is a workaround for consumption.

If the manufacturers printed the consumption figures on the date badge then the app / calculation wouldn't even be needed as you could just x the 2 min test period by 30 and you'd end up with the hourly consumption in m3/hr or ft3/hr (at max rate of course)
 
Last edited:
In reality the cv of the gas doesn't really affect your calculations as all you are checking is that the boiler is passing the correct amount of gas.
Injectors are sized to pass a certain amount of gas at a certain pressure and zpg's set to draw the correct amount of gas nearly no matter what the inlet pressure is (unless it is very low). That is (should be) the constant you are checking against what the manu says it should work out at.
You have no way of knowing the actual HI of the boiler as that is the variable (due to the cv).
It just means if you live somewhere with a high cv your combi will give a bit better hot water and if you live in London your onto plumbs as your cv is generally lower :lol:

Btw i had a job last year where the incoming pressure was below 10mb (water in the service) and the boiler gas rated and was running perfect! Work that one out¿¿¿
 
Btw i had a job last year where the incoming pressure was below 10mb (water in the service) and the boiler gas rated and was running perfect! Work that one out¿¿¿

was it running on fumes from a hungover buckfast swigging jock? :29:
 
In reality the cv of the gas doesn't really affect your calculations as all you are checking is that the boiler is passing the correct amount of gas.
Injectors are sized to pass a certain amount of gas at a certain pressure and zpg's set to draw the correct amount of gas nearly no matter what the inlet pressure is (unless it is very low). That is (should be) the constant you are checking against what the manu says it should work out at.
You have no way of knowing the actual HI of the boiler as that is the variable (due to the cv).
It just means if you live somewhere with a high cv your combi will give a bit better hot water and if you live in London your onto plumbs as your cv is generally lower :lol:

Btw i had a job last year where the incoming pressure was below 10mb (water in the service) and the boiler gas rated and was running perfect! Work that one out¿¿¿

And this is exactly the point I was making above.
 
Last edited:
In reality the cv of the gas doesn't really affect your calculations as all you are checking is that the boiler is passing the correct amount of gas.
Injectors are sized to pass a certain amount of gas at a certain pressure and zpg's set to draw the correct amount of gas nearly no matter what the inlet pressure is (unless it is very low). That is (should be) the constant you are checking against what the manu says it should work out at.
You have no way of knowing the actual HI of the boiler as that is the variable (due to the cv).
It just means if you live somewhere with a high cv your combi will give a bit better hot water and if you live in London your onto plumbs as your cv is generally lower :lol:

Btw i had a job last year where the incoming pressure was below 10mb (water in the service) and the boiler gas rated and was running perfect! Work that one out¿¿¿

Why would you gas rate a boiler which has 10mb incoming pressure and water in the service.


Sent from my iPad using Tapatalk HD
 
Why would you gas rate a boiler which has 10mb incoming pressure and water in the service.


Sent from my iPad using Tapatalk HD
Maybe he rated it before he found the water?

Normally put my gauge on the boiler to measure incoming pressure at the same time as a gas rate so they correlate, not un thinkable I'd imagine.
 
Why would you gas rate a boiler which has 10mb incoming pressure and water in the service.

Because i'd just fitted it and was commissioning it of course.

Guage on the boiler and fired it up. Dropped down to below 10 straight away. Guage on the meter (3 ft away), bouncing between about 8 and 12mb. I rated it out of curiosity. It was perfect.
Boiler was a 30si.
Water gets into the mains sometimes up here and can work itself into the service. If you disconnect the ecv you can hear it gurgling and sometimes you can get some out.
SGN cut the pipe in the street and blew it with the compressor.
 
Because i'd just fitted it and was commissioning it of course.

Guage on the boiler and fired it up. Dropped down to below 10 straight away. Guage on the meter (3 ft away), bouncing between about 8 and 12mb. I rated it out of curiosity. It was perfect.
Boiler was a 30si.
Water gets into the mains sometimes up here and can work itself into the service. If you disconnect the ecv you can hear it gurgling and sometimes you can get some out.
SGN cut the pipe in the street and blew it with the compressor.

So it was just out of curiosity?
I wouldn't have bothered, you can't commission the boiler with only 10mbar at the inlet and water in the service.
 
Status
Not open for further replies.

Reply to Gas rate app in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi everyone, My customer has a gas fire (Gazco Logic HE fire, about 10 years old). It's a slide control fire. The fire has become difficult to...
Replies
1
Views
315
Hello, I have quite low flow rate for my electric shower (a piddling 5L/min), and would like some tips or advice about how to solve or find the...
Replies
14
Views
894
Essaboy
E
I'm looking for a commercial gas engineer to assist with servicing, callouts etc. work is mostly london based but also have sites in kent/essex...
Replies
1
Views
1K
Neil Ambrose
N
i am a landlord and have had great advice here. I am using a new gas engineer/plumber who tells me Water Quality testing is now a compulsory part...
Replies
2
Views
282
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
564
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock