Hi all,

I am currently in the process of completing my Gas portfolio and have just started to complete some installs.

I have a question regarding gas rate/heat input on a Glow worm Energy 12r which I am currently installing.

I would like to know which Kw figure I use to compare my calculated heat input too. I put the boiler into high mode and timed 1 revolution on the imperial meter at the property.

Do I use the maximum heat-input for heating or maximum heat-input for hot water? I can't find a rate for the boiler when its running at maximum rate.

Any help would be much appreciated.

below is a screen shot from the manual

thumbnail_IMG_2267.png
 
If the boiler is set into test mode Qnw should be 15.3Kw - 1.62m3/hr. It will be clearly stated in the MI’s - but maybe not in the specification sheet that you have pictured. Read the section in the MI’s which should outline how to undertake the Gas Rate test and the specification of acceptable results
 
Last edited:
If JimmyP is installing the boiler and checking the gas rate, he shouldn't. The person who is mentoring (qualified gas engineer) should be, and would know where and how to look.
 

Reply to Gas Rate Advice please in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
535
  • Article
A Plumber Who Worked Illegally Gets A Suspended Sentence After Falsely Claiming To Be Gas Safe Registered. A Plumber in Herefordshire was...
Replies
0
Views
228
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to...
Replies
9
Views
273
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
190
I am in process of replacing an existing sink with a new stainless steel one. The existing tap is plumbed directly to copper which means that it...
Replies
6
Views
293
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock