Francis.

Engineer
Messages
12
This is on my self build project.
6 loops of 120M each were laid on insulation in 100mm concrete screed.
The manifold was installed & pressure tested before the concrete was laid & held for a long time after.
That was over two years ago & the building has had no heating in all this time.
Just installed a new ground source heat pump & immediately found a split pipe at the manifold.
On repairing this pipe we have tried pressuring the system & found major leaks on 3 out of the 6 circuits, one so bad that no pressure at all reads with the filling loop fully on.

my options 1. resign myself to only running 3 loops... not good as the room with the canbus temp sensor won't be heated.
2. try leak sealer products .... doubt they'd be much good at the flow rate I'm loosing.
3. listen for the sounds of the leaks & dig them up ... not good spent a fortune on granite tiles.
Major delay on heating partially from ICE energy going bust & taking my deposit with them..
More than a bit depressing right now....
 
CEMEX evolution liquid concrete.. basically 10mm aggregate loads of plasticiser & flowable.
The pipe is Wunda 16mm pe-al-pe cable tied to 50mm squared galvanised mesh.
The pressure test went to over 10 bar... set at 6 but the heat of the cure sent it off the gauge, was still all good a month later though..
Should have blown all the test water out... Should have used better quality pipe..
Up a creek without a paddle on this one...
 
Very unusual mate what brand of underfoor piping did you use hard to believe the leaks were caused by frost in the screed above ground maybe any pictures ? Cheers kop
 
Can't see it being frost damage in the concrete. Nowhere for pipe to expand and split. Leak sealer is a no go.

If it's that bad then either dig it all up and start again or stick some radiators in to boost the three loops.
 
photos of installation.... I'm going to try digging up some floor after listening to the leaks.. the sound does travel a lot.
The pipes are sleeved for about 600mm between room slabs. really odd no sign of water anywhere & its all on a dpm as well.
DCP00530.JPG
DCP00531.JPG
DCP00535.JPG
 
I'd agree, the only solution is to dig it up and start again or re-lay on top of the failed floor if there's sufficient height.

I wouldn't trust using any of the non leaking loops.
 
Cant see to much wrong there really mate bit of a mystery that one , the most cost effective way would be to put a overlay system on the top its to much work to dig it all up , but i guess the project has moved on a bit since the pictures best of luck with it cheers kop.
 
It's fair to say the floors don't look the same, getting the heating up & running has been left to last in a long list of work.
Anyone got a time machine ???
Blowing air through the faulty lines might give me a clearer sound to trace, a serious amount of water has gone somewhere under the slab & not even a trace of damp, not that I really want to soak the place..
More photos to show what I'm up against as regards starting in with a jack hammer.
DCP00780.JPG
DCP00781.JPG
DCP00782.JPG
DCP00783.JPG
DCP00784.JPG
 
nice looking place mate you are well and truly stuffed though don't dig up you will wreck the place and if you find a leak and do a repair it will just find the next weakest point and leak there take the hit replace it have a look at uheats website on here and price up a overlay system all that needs doing is trim the doors and plinths then I know you will have to replace your tiles but it will still work out cheaper and cause less disruption and be guaranteed no leaks , you should not put the heating loops under the kitchen units or bathroom furniture . cheers kop
 
Status
Not open for further replies.

Reply to Frost damage to underfloor heating pipes. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
505
losing pressure
L
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m...
Replies
6
Views
326
Hi guys. I've been running an UFH installation/ repair business for 7 years now and one of my main frustrations is finding the parts for the UFH...
Replies
1
Views
217
Hello all, I have a WorcesterBosch Greenstar 42CDi classic combi, which is providing DHW fine, but not heating. Was working fine in spring...
Replies
11
Views
1K
Hi everyone, I moved into a new build three bedroom, two bathroom bungalow about 2.5 years ago. Ever since we moved in there has been an issue...
Replies
70
Views
6K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock