Hi there,

I am making connection to the backboiler on a Rayburn. It has 1"BSP female threads. I understand I need to use male BSP iron connectors with fibre washers.

I need the flow pipe to exit and immediately turn a sharp right angle downwards, in order to avoid part of the fitted kitchen. I do not have room to use a compression fitting and bend the pipe, so I propose to use a 90 deg BSPM to compression. However, how can I ensure that it will end up facing the right direction when tightened?

Two proposals which occur to my non-plumbers brain, are:

1) To pack the thread with additional washers until the angle is correct. I suppose it is possible, knowing the thread pitch to calculate the washer thickness required to rotate a required angle?

2) To thread a backnut onto the male thread before connecting to the boiler, and use it to tighten the fitting once correct angle is achieved. Concerned this may leave me with insufficient thread to make a secure connection between fitting and boiler.

I look forward to more experienced replies.

Many thanks
 
Loctit 55 or 557 you can set these at any angle, so you can wind the elbow all the way in and back it off 1/2 a turn if it doesn't line up where you want it
 
The flow pipe I speak of is the exit from the backboiler. It is an open vented system, with a header tank elsewhere in the loop.
 
The flow pipe I speak of is the exit from the backboiler. It is an open vented system, with a header tank elsewhere in the loop.

If there is just the one flow, it will include the vent. It must rise all the way.
Do you know what I mean by vent?
 
Sounds like your trying to angle the flow downwards on a gravity feed system?
 
the system is pumped. Not sure where the idea that it was gravity came from, unless just an assumption because it's a rayburn?

System is in a boat, rads layed out over a 10m horizontal run with windows and doors in the way, which pipework has tp run under, no room for the rise required by gravity, so system is pumped.
 
System is in a boat, rads layed out over a 10m horizontal run with windows and doors in the way, which pipework has tp run under, no room for the rise required by gravity, so system is pumped.
Sounds to me like your Rayburn has a back boiler and this flow pipe you speak of will send hot water to the radiators - Yes?
Sister lives on a boat with a Squirrel stove and back boiler which does the same with 22 or 28mm shiny copper pipe. Advise checking maximum distance and rad sizes that the pump can deal with before going further.
 
Sounds to me like your Rayburn has a back boiler and this flow pipe you speak of will send hot water to the radiators - Yes?
Sister lives on a boat with a Squirrel stove and back boiler which does the same with 22 or 28mm shiny copper pipe. Advise checking maximum distance and rad sizes that the pump can deal with before going further.

Are these sealed RPM.?
 
Duraglit for Christmas!
She has that amongst other cleaning stuff, considering it is basically 6ft wide x 50ft long open plan with her, 2 dogs and a wood burner with yards of copper pipe on display and wood floor it is immaculate.
 
She has that amongst other cleaning stuff, considering it is basically 6ft wide x 50ft long open plan with her, 2 dogs and a wood burner with yards of copper pipe on display and wood floor it is immaculate.

Ask her if I can borrow it for mi holidays. I looked at renting one, have you seen the prices for a week?
Not cheap but I’d love to have a do!
 
Ask her if I can borrow it for mi holidays. I looked at renting one, have you seen the prices for a week?
Not cheap but I’d love to have a do!
Not a chance in hell mate! Do it and de stress for a week, recommend the Norfolk Broads because it is so large and no frustrating locks where you have to queue for ages to get through in the summer.
 
If the Rayburn is solid fuel, what happens when the pump fails?
Where is the safety?

Hello there Best.
Good question. Do you know if these are sealed or open vented, or do they have a different set up?
 
OK, I am no plumber (as you may have gathered) but have boated for a while... Have consulted various (many boat specific) plumbers in design of this system. It is as follows:

Rayburn with backboiler, output to 22mm copper pipe for first few meters, then switch to plastic. Three rads and hot water cylinder (calorifier) all connected in parallel. One of the rads (in bathroom) has no TRV, so is always on as a safety. Header tank is T-d off of return pipe, it is highest point in system, used as filler and check point, it also has overflow. Pump on return line to back boiler.

I am given to understand that in the event of pump failure system may boil. Header tank will overflow if boiling is significant enough. I am also led to believe that many systems, even those with (for example...) pipes which turn immediately downwards as they exit the back boiler, will still thermosyphon even when physics and logic suggests that they shouldn't.

After I exit the boiler and turn the pipe downwards I will curve the pipe so that it is running horizontal, so I am effectively creating a dogleg of a few inches.

I will not be polishing any of my copper pipe.
 
I don't see how the boiler will thermosyphon if pipes exiting boiler are to be turned downwards. Boiler will just boil like a kettle and vibrate if pump or power fails. At least that's what has happened to jobs I have seen and heard about which had the solid fuel boiler pipes dropped downwards by diyers or incompetent plumbers.
 
Ok, well I am clearly both a DIYer and incompetent plumber, but keen not to be if at all possible... Perhaps you can help?

Top pipe exits rayburn boiler immediately into the side of a stainless steel sink unit (50mm gap only). The onward journey of the pipe follows under the sink unit for 1800mm, there is no logical way of it happening above the level of the sink.

Only potentially useful thing I can think of is to move the header tank (proposed as a T off the system) and site it above the exit to the boiler. That way in the event of a pump failure coolant could boil up to the header tank, and overflow could be routed down to sink draining board? I could place a Tee fitting on the exit of the boiler, with flow pipe going downwards, routed under sink, and upwards facing end feeding the tank?

Thoughts?
 
I would want " boil up " to be kept controlled by heat loss somewhere - to a hot water cylinder plus one radiator (or more) piped for same.
Pity the flow couldn't be installed rising in that 50mm space?
The whole thing scares me tbh. Best to get a solid fuel heating installer to also have a look at the place
 
Status
Not open for further replies.

Reply to Connecting BSP iron threads at specific angle in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it 😬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
268
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
189
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
213
S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and pebbles!) We saw that the pipe that takes water down the gutter was visibly full to the top. He said he will return with a coil to push through...
Replies
1
Views
67
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
479
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock