People, please can I have your help on a circulation issue (these are the issues I struggle with more than anything)?

Here goes:
- system is open vented y plan
- new pump has been installed
- new three port valve with actuator has been installed
- system has been powerflushed properly
- but still poor circulation / boiler locking out with F25 error
- I can feel heat on the flow on the DHW Cyc but nothing on the return
- also feel heating just after zone valve but nothing another 0.3m down the pipe
- checked the pipework in the airing cupboard with a magnet & found no signs of magnetic force. So I'm thinking cold feed is ok
- system doesn't circulate on HTG or DHW, boiler shoots from 20-80 degrees in seconds
- when it doesn't lock out, it gets to temp then burn goes off. Then comes on again.........
Any suggestions, your assistance would be greatly appreciated
 
Nrv on the pipework sometimes
 
Would say on the primary return/ by the airing cupboard

You sure you have no air locks in the return?
 
Would say on the primary return/ by the airing cupboard

You sure you have no air locks in the return?
Could be an air lock I'm not sure. I did shut off a Rad then replaced the bleed valve with a pipe. Then opened both valves at diff times, wouldn't that have cleared the air lock.

Plus customer has had this issue for a while, I'm the 3rd person who has worked on the system
 
Is there a drain point at the boiler ?
 
Pump on the flow ?
Maggy on return?
 
Sounds like an horrendous air lock. If there's a drain point low down on the system you could try emptying it then back-filling from the ground up. You'll need someone in the lord keeping an eye on the level in the f&e though...
 
Sounds like an horrendous air lock. If there's a drain point low down on the system you could try emptying it then back-filling from the ground up. You'll need someone in the lord keeping an eye on the level in the f&e though...
I have already isolated a Rad, then connected a hose to the outside. Then opened 1 end at a time for a few mins.

Wouldn' that have cleared an air lock???
 
What boiler is it? I’ve had circular heat exchangers badly blocked to the extend that they needed replacing.
 
you could have a restriction in the heat exchanger happened to me recently on a valliant . cheers kop
 
I had a issue similar a few week back,
Turned out that the ERP pump was faulty
The digital screen display looked like the pump was running and in fact would intermittently but ultimately would stop and the display would stay the same.
Pcb in pump frazzled and replaced with a standard pump

Sorted issue
 
Status
Not open for further replies.

Reply to Circulation Issues, pls help in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

B
Context for issue: I'd like to start by saying I'd rather not read 100 "Hire a professional comments", I will do that when/if it comes to it, but...
Replies
0
Views
381
Butchy10
B
Context for issue: Last winter the temperature switch on my boiler shorted somehow, the boiler was then running WAY too hot and ended up...
Replies
6
Views
604
Desperate for some help! Be a life saver of someone can help as suffer from a high intolerance to noise. Moved into new house 1940s (copper...
Replies
7
Views
811
C
Hi, I'm English and live in the Czech Republic and I'm having difficulty with my heating system. Unfortunately, I cant find any heating engineer...
Replies
1
Views
657
Hello, recently our boiler stopped working properly, causing a lack of heat in our 14-radiator splitter in 3 storeys. having only one boiler at...
Replies
4
Views
430
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock