Evening all,
I've just changed a Keston system boiler for a regular Worcestor with a pump. The customer had bought the boiler mistakenly thinking it was a like for like swap. I've added the pump and everything seemed fine but a week later he's complaining about air in the system and the F&E tank overflowing. I'd replaced the float valve and probably didn't bend the arm enough as there wasn't a lot of room for a 18 rad system. I've adjusted the arm further. I suspect the air is being sucked in through the vent. It's an S plan in a three storey house with the boiler and cylinder in a cupboard on the middle floor. The pump is on the flow pipe. The rads are all knackered and he didn't want a powerflush as he didn't think they would stand it. I agreed and tried to flush as much of the sludge out with detergent. I've turned the pump down. Has anyone any ideas what I can do? From distant memory I seem to think a 'wet vent' might be the answer but I can't remember how to do one. Any advice appreciated.

Jock.
 
You will have to close couple the feed / vent etc .
First pipe off the flow pipe , next vent , next pump . All within 150 mm .
Currently on the flow there's a 15mm stem pipe to an auto air vent above the boiler teed in before the pump. Are you suggesting teeing in the feed, then the vent before the pump and should I dispense with the stem pipe?
 
Currently on the flow there's a 15mm stem pipe to an auto air vent above the boiler teed in before the pump. Are you suggesting teeing in the feed, then the vent before the pump and should I dispense with the stem pipe?

I would yes , the close coupling system works . As said , feed first , immediately after vent , then pump , all on flow pipe , that wont suck any air in as its all under positive pressure . Ok a bit of work involved I will admit .
 
Like this?
Open-System-Header-Tank.gif
 

Reply to Central heating sucking air through vent pipe in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
462
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m...
Replies
6
Views
321
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16...
Replies
0
Views
240
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
560
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to...
Replies
6
Views
289
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock