Any1 know the rules about fitting a boiler in an under stairs cupboard?
 
What rules ? are there sum ? no probs as i see it

Refer to BS6798 as follows:4.4
Location
COMMENTARY AND RECOMMENDATIONS ON
4.4
Room‑sealed boilers may be installed in any room or space. It is not
recommended that any type of boiler be installed in an understairs
cupboard, bathroom or shower room, bedroom or bed-sitting room, or
within a toilet or cloakroom, but such installations are acceptable subject
to the requirements of
5.3.4 to 5.3.7.
5.3.4
Understairs cupboard installations
If a boiler is installed in an understairs cupboard, the cupboard shall
conform to one of the following.
Where the premises in which the cupboard is a) located has no more
than two storeys, the cupboard shall conform to
5.3.2.
b) Where the premises in which the cupboard is located has more
than two storeys, all the internal surfaces of the cupboard,
including the base, shall be non‑combustible or lined with
non‑combustible material, having a fire resistance of not less
than 0.5 h when determined in accordance with BS 476‑22 and
the air vents shall be direct to outside air.
COMMENTARY AND RECOMMENDATIONS ON
5.3.4
Installation in an understairs cupboard should only be considered if there
is no alternative location.
Whenever possible, the boiler in an understairs cupboard should be of the
room‑sealed type.
 
British Standard 6798Specification for installation
and maintenance of gas-fired
boilers of rated input not
exceeding 70 kW net
 
Refer to BS6798 as follows:4.4
Location
COMMENTARY AND RECOMMENDATIONS ON
4.4
Room‑sealed boilers may be installed in any room or space. It is not
recommended that any type of boiler be installed in an understairs
cupboard, bathroom or shower room, bedroom or bed-sitting room, or
within a toilet or cloakroom, but such installations are acceptable subject
to the requirements of
5.3.4 to 5.3.7.
5.3.4
Understairs cupboard installations
If a boiler is installed in an understairs cupboard, the cupboard shall
conform to one of the following.
Where the premises in which the cupboard is a) located has no more
than two storeys, the cupboard shall conform to
5.3.2.
b) Where the premises in which the cupboard is located has more
than two storeys, all the internal surfaces of the cupboard,
including the base, shall be non‑combustible or lined with
non‑combustible material, having a fire resistance of not less
than 0.5 h when determined in accordance with BS 476‑22 and
the air vents shall be direct to outside air.
COMMENTARY AND RECOMMENDATIONS ON
5.3.4
Installation in an understairs cupboard should only be considered if there
is no alternative location.
Whenever possible, the boiler in an understairs cupboard should be of the
room‑sealed type.
where is 5.3.2 ? pls
 
5.3.2.
b) Where the premises in which the cupboard is located has more
than two storeys, all the internal surfaces of the cupboard,
including the base, shall be non‑combustible or lined with
non‑combustible material, having a fire resistance of not less
than 0.5 h when determined in accordance with BS 476‑22 and
the air vents shall be direct to outside air.

5.3.7 does not apply to understairs cupboards


Read more: http://www.ukplumbersforums.co.uk/g.../49040-boiler-under-stairs.html#ixzz2MCEUx0A5
 
Sorry my mistake. If the property has less than two floors then there is no requirement to fire proof. Its about fire regs. You can jump from a first floor and probably survive, but less chance from a second floor.
5.3.2.1

The boiler compartment shall be a fixed rigid structure, the
internal surfaces of which conform to the boiler installation instructions.
COMMENTARY AND RECOMMENDATIONS ON
5.3.2.1
If the boiler manufacturer’s installation instructions do not give specific
advice, then any internal surface of the boiler compartment which is of
combustible material should either be at least 75 mm from any part of
the boiler or should be lined with non-combustible material. Methods
of determining whether a material can be described as combustible
or non-combustible are given in BS 476-22. For further advice, see
HSE publication,

Safety in the installation and use of gas systems and
appliances

5.3.2.2The compartment shall permit access for inspection and servicing
of the boiler and any ancillary equipment. A notice shall be fixed in a
prominent position within the compartment to warn against its use as
a storage cupboard. The compartment shall be fitted with a door that
will permit withdrawal of the boiler and any ancillary equipment.
 
Status
Not open for further replies.

Reply to Boiler under stairs in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have decided to remove the timber floor boards and joists as they are effected by damp and rotting. Was hoping to infill and have slab and...
Replies
2
Views
353
I am buying a new house and I wondered if it was possible to put a washing machine and condenser dryer under the stairs
Replies
3
Views
2K
Hi all, sorry about the long post but a novice here looking for some advice... I've just bought a 12 bedroom private house with 3 bathrooms that...
Replies
3
Views
570
T
I am fitting a 80 lt back up emersion, flat tank it's back up while I interview the existing gas boiler, mechanically not gas wise. I only have 14...
Replies
1
Views
332
Hi, I need some urgent advice. I've Just come home after going out for evening, to discover hallway floor and kitchen floor covered in water. On...
Replies
1
Views
531
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock