Any1 know the rules about fitting a boiler in an under stairs cupboard?
 
What rules ? are there sum ? no probs as i see it

Refer to BS6798 as follows:4.4
Location
COMMENTARY AND RECOMMENDATIONS ON
4.4
Room‑sealed boilers may be installed in any room or space. It is not
recommended that any type of boiler be installed in an understairs
cupboard, bathroom or shower room, bedroom or bed-sitting room, or
within a toilet or cloakroom, but such installations are acceptable subject
to the requirements of
5.3.4 to 5.3.7.
5.3.4
Understairs cupboard installations
If a boiler is installed in an understairs cupboard, the cupboard shall
conform to one of the following.
Where the premises in which the cupboard is a) located has no more
than two storeys, the cupboard shall conform to
5.3.2.
b) Where the premises in which the cupboard is located has more
than two storeys, all the internal surfaces of the cupboard,
including the base, shall be non‑combustible or lined with
non‑combustible material, having a fire resistance of not less
than 0.5 h when determined in accordance with BS 476‑22 and
the air vents shall be direct to outside air.
COMMENTARY AND RECOMMENDATIONS ON
5.3.4
Installation in an understairs cupboard should only be considered if there
is no alternative location.
Whenever possible, the boiler in an understairs cupboard should be of the
room‑sealed type.
 
British Standard 6798Specification for installation
and maintenance of gas-fired
boilers of rated input not
exceeding 70 kW net
 
Refer to BS6798 as follows:4.4
Location
COMMENTARY AND RECOMMENDATIONS ON
4.4
Room‑sealed boilers may be installed in any room or space. It is not
recommended that any type of boiler be installed in an understairs
cupboard, bathroom or shower room, bedroom or bed-sitting room, or
within a toilet or cloakroom, but such installations are acceptable subject
to the requirements of
5.3.4 to 5.3.7.
5.3.4
Understairs cupboard installations
If a boiler is installed in an understairs cupboard, the cupboard shall
conform to one of the following.
Where the premises in which the cupboard is a) located has no more
than two storeys, the cupboard shall conform to
5.3.2.
b) Where the premises in which the cupboard is located has more
than two storeys, all the internal surfaces of the cupboard,
including the base, shall be non‑combustible or lined with
non‑combustible material, having a fire resistance of not less
than 0.5 h when determined in accordance with BS 476‑22 and
the air vents shall be direct to outside air.
COMMENTARY AND RECOMMENDATIONS ON
5.3.4
Installation in an understairs cupboard should only be considered if there
is no alternative location.
Whenever possible, the boiler in an understairs cupboard should be of the
room‑sealed type.
where is 5.3.2 ? pls
 
5.3.2.
b) Where the premises in which the cupboard is located has more
than two storeys, all the internal surfaces of the cupboard,
including the base, shall be non‑combustible or lined with
non‑combustible material, having a fire resistance of not less
than 0.5 h when determined in accordance with BS 476‑22 and
the air vents shall be direct to outside air.

5.3.7 does not apply to understairs cupboards


Read more: http://www.ukplumbersforums.co.uk/g.../49040-boiler-under-stairs.html#ixzz2MCEUx0A5
 
Sorry my mistake. If the property has less than two floors then there is no requirement to fire proof. Its about fire regs. You can jump from a first floor and probably survive, but less chance from a second floor.
5.3.2.1

The boiler compartment shall be a fixed rigid structure, the
internal surfaces of which conform to the boiler installation instructions.
COMMENTARY AND RECOMMENDATIONS ON
5.3.2.1
If the boiler manufacturer’s installation instructions do not give specific
advice, then any internal surface of the boiler compartment which is of
combustible material should either be at least 75 mm from any part of
the boiler or should be lined with non-combustible material. Methods
of determining whether a material can be described as combustible
or non-combustible are given in BS 476-22. For further advice, see
HSE publication,

Safety in the installation and use of gas systems and
appliances

5.3.2.2The compartment shall permit access for inspection and servicing
of the boiler and any ancillary equipment. A notice shall be fixed in a
prominent position within the compartment to warn against its use as
a storage cupboard. The compartment shall be fitted with a door that
will permit withdrawal of the boiler and any ancillary equipment.
 
Sorry, no link to this one. You would have to subrscibe to BSI to get their documents, but they are extremely expensive. I can see some of them but they are all controlled by copy write.
 
Status
Not open for further replies.

Reply to Boiler under stairs in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Can anyone recommend a decent multi meter, preferably under a 100 pounds. It's for checking boiler components so I don't need a top spec one ....just easy to use and reliable. The fluke 115 looks good but its above my budget. My current socket and see one was great but it's developed a fault.
Replies
7
Views
223
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
143
  • Article
A Plumber Who Worked Illegally Gets A Suspended Sentence After Falsely Claiming To Be Gas Safe Registered. A Plumber in Herefordshire was prosecuted after Hereford Trading Standards Team found that he was falsely claiming to be on the Gas Safe Register when he was not, putting members of the...
Replies
0
Views
130
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
200
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
257
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock