Hi everyone

Summary is in the title. Found the boiler was at 0.5 bar earlier today so topped up to 1.5 bar. Checked before bed and its back to 0.5 bar.

There are no signs of a leak around any radiators nor any suspicious water damage on the downstairs ceiling.

Before I rip up all the flooring downstairs to find a leak going into the cavity under the house, what other things could be causing this?
 
Last edited:
Your boiler will have a PRV (pressure relief valve) which lifts at 3.0 bar, you should see a small bore waste pipe from this PRV maybe exiting the wall at the rear of the boiler. Tiewrap or tape a plastic bag on the end of this and check for water regularly, also watch boiler pressure while the system is heating up and note the pressure rise, a 0.5/0.7 bar would be typical but if approaching 2.8bar then problem somewhere, probably E.vessel.
 
Your boiler will have a PRV (pressure relief valve) which lifts at 3.0 bar, you should see a small bore waste pipe from this PRV maybe exiting the wall at the rear of the boiler. Tiewrap or tape a plastic bag on the end of this and check for water regularly, also watch boiler pressure while the system is heating up and note the pressure rise, a 0.5/0.7 bar would be typical but if approaching 2.8bar then problem somewhere, probably E.vessel.
Thanks for the reply.

The only copper pipe comes out of the outside wall below the flue, and then goes straight back inside the wall.
 
If this is less than say 1/2 ins then it might only seem to go back in, it might only be turned back in with its open end almost up against the wall.
You're absolutely correct, have just tied a bag to the end of that pipe and topped system up again to 1.5 bar (was just below 0.5 bar). With heating on, pressure rose to close to 2.5 bar within 10 minutes, then boiler shut off even though thermostat was not at its target temperature. Does this support the expansion vessel being the issue?
 
If no water bagged by morning and if no system leak then possibly boiler heat exchanger, if you can locate the boiler condensate pipe (on the instreuction/user manual) then with boiler shut down for a few hours you might be able to break a connection on this pipe and see if water dripping from it.
 
If no water bagged by morning and if no system leak then possibly boiler heat exchanger, if you can locate the boiler condensate pipe (on the instreuction/user manual) then with boiler shut down for a few hours you might be able to break a connection on this pipe and see if water dripping from it.
This isn't a condensing boiler as far as I know, so don't think it would have a condensate pipe?
 
If no water bagged by morning and if no system leak then possibly boiler heat exchanger, if you can locate the boiler condensate pipe (on the instreuction/user manual) then with boiler shut down for a few hours you might be able to break a connection on this pipe and see if water dripping from it.
Pressure has dropped back to about 0.8 bar and there is some water in the bag. Does this look about right for the amount of water for a c. 1.5 bar drop in pressure?
 

Attachments

  • PXL_20230113_131701191.jpg
    PXL_20230113_131701191.jpg
    784.5 KB · Views: 9
Hard to say but good in one sense that the PRV is leaking.
So... assume a 8ltr EV with precharge and filling pressures of 0.8/1.5bar, the EV/system would have to loose 2L to fall to 0.8bar but if the EV effective volume is only 1/2 due to loosing air out of the EV (airend) then it it only has to loose 1L under the same conditions and so on.
Would suggest fill to 1.5bar, then open a rad vent and keep bleeding water into a container until the pressure falls to 0.8/1bar and measure it, that will tell (almost) all.
 

Reply to Baxi Combi 105e: CH lost 1 bar of pressure in a few hours in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
132
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
186
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
194
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
231
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock