Im an installer in glasgow who came across this on an installation im looking for opinions and any advice from guys/ gals who have seen anything like this HUTCHISON STREET N0 2.jpg
 
These are exhaust flues of a ferroli modena 80 e , 15 mtres throughout the building they are not insulated, they are not ferroli terminals, water pours in through them and down into the boiler, i classed the boiler as at risk and shut it down, and recommended a new boiler which would cope with the condensation travellling down the exhaust part of the flue and prevent rain entering it
 
That is shocking! Internal flue used externally and a modification to the flue!

Kendod, PM Gasman with your Gas Safe details and you'll be granted access to the private gas safe forum.
 
lads thats nothing got a better one than these photos,View attachment 11808 the only reason use can see this flue terminal is that has just sucked up all the co gases produced by the other boilers, this my friends was over looked by gas safe..... and will shortly be posting a mind *** of information here that has cost me roughly between 30 and 40 grands worth of work by........ GAS SAFE, the registeredbody who infact do not tell you how it is done, it is youre manufacturors who will tell you how an appliance should be fitted, and looked after GAS SAFE are just a policing body for registered engineers not youre illegal gas workers................
 
Last edited by a moderator:
lads thats nothing got a better one than these photos,View attachment 11808 the only reason use can see this flue terminal is that has just sucked up all the co gases produced by the other boilers, this my friends was over looked by gas safe..... and will shortly be posting a mind *** of information here that has cost me roughly between 30 and 40 grands worth of work by........ GAS SAFE, the registeredbody who infact do not tell you how it is done, it is youre manufacturors who will tell you how an appliance should be fitted, and looked after GAS SAFE are just a policing body for registered engineers not youre illegal gas workers................
 
hi buddy just checking to see if you got my message just new on here
 
Status
Not open for further replies.

Reply to At risk or not to current standered use decide in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Home owner looking for some advice pls. We have a megaflow system which we are considering removing as the tank takes up a lot of space and we...
Replies
2
Views
226
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
563
Had conventional boiler and tanks removed last year and new combi fitted and just recently had it serviced but the guy who did it has given me a...
Replies
9
Views
785
I am looking into a new Main eco compact / Baxi 618 system boiler set up for PDHW (if its possible) I was hoping to use the EPH controls priority...
Replies
1
Views
385
Im looking to install a saniflo or similar, with the outlet rising up through a flat roof and into a soil stack above. The problem is, this...
Replies
18
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock