Doing a bit of a revamp of heating system some rads out new ones in . Took old galvanised expansion tank out of loft. Now I reckon this thing had a capacity of a good 100 litres. Looking at replacements they seem to be 18 litre and that is it. Now I have some 22 rads and what with a run to and from the boiler I recon there is roughly about 300 litres in the system. Using an online calculator it states that my 300 litres say at 5degC will be 317 litres at 75degC. Will not be this as obviously water might leave the boiler at 75degC but the return might be only around 45deg C so average is 60degC hence an averaged rise of 55degC for the sake of calculations. This give a heated volume now of 313.5 litres ie expansion of 13.5 litres.All this is leading to is an 18 litre expansion tank sufficient for my volume of water? If not is there an alternative to not using a cold water cistern sized thing which is way oversized?
Thanks
 
You sure it was an f and e tank and not supplying your cylinder (for your hot water) ?

Also by the looks of your post your out of your depth as that calc is for a sealed system

My best advice is get a gas safe engy in
 
Definitely expansion tank the water tank is next to where the expansion tank was. Not sure how you think my figures are for a sealed system.
 
If what you are saying is correct - just go an purchase a 24 litre expansion tank.
Could be an overkill - but it will work.
I did some oldschool calcs - 18 should be fine but if it were me, I would put in a 24.
 
I would if I could find one. Here we seem to go from 18 litres straight to 114 litres ie 25 gallons
 
Are we not at apples and pears here. Assuming the expansion tank in the loft is for a vented gravity system and the tanks he is looking at are pressure vessels for an unvented sealed system ? although i dont have any trouble sizing vessels in small increments here
 
Now I have some 22 rads and what with a run to and from the boiler I recon there is roughly about 300 litres in the system.

That seems rather a lot. Between two and three times what I'd expect for a domestic system. DId you measure it by counting buckets when you drained it?

How big was the old expansion tank? If you look carefully inside it you can probably see the high-water and low-water levels represented by rings of crud and corrosion.
 
Are we not at apples and pears here. Assuming the expansion tank in the loft is for a vented gravity system and the tanks he is looking at are pressure vessels for an unvented sealed system ? although i dont have any trouble sizing vessels in small increments here
No tanks am looking at are for gravity fed system.
 
That seems rather a lot. Between two and three times what I'd expect for a domestic system. DId you measure it by counting buckets when you drained it?

How big was the old expansion tank? If you look carefully inside it you can probably see the high-water and low-water levels represented by rings of crud and corrosion.
I think I am not too far of the volume. Worked it out by radaiator size and then adding volume in pipework. The boiler is some 15m plus away from the house and feed and return are in 32mm plus there is a fair bit of 28mm and 22mm knocking about soon adds up. Old expansion tank was I reckon a good 100 litres minimum has been at the tip for weeks so no chance of looking at levels.
 
I think I am not too far of the volume. Worked it out by radaiator size and then adding volume in pipework. The boiler is some 15m plus away from the house and feed and return are in 32mm plus there is a fair bit of 28mm and 22mm knocking about soon adds up. Old expansion tank was I reckon a good 100 litres minimum has been at the tip for weeks so no chance of looking at levels.

Fair enough. As a rule of thumb, you want 10 cm depth of water in the FE tank when the system is cold and then space for an additional 5% of the system water to expand into. So, by this method you would need a bit more than 18 litre.

Polytank, for example, do 55 litre rectangular tanks in three shapes:

RECTANGULAR

I'd consider a single tank as a nicer solution than two 18 litres linked into a pair. The footprint will be smaller and easier to install and insulate.

The fact that the previous tank was 100 litre suggests that the previous installer decided (or discovered!) that a standard 18 litre (4-gallon) FE wasn't big enough.

[Afterthought: Check before buying that Polytank approves use of their rectangular tank as a CH FE application. I'm 99% sure they're suitable, but I can't find it explicitly specified on the website.]
 
Last edited:
Strangely enough I had seen their tanks before online and at the back of my mind thought might be the solution. They have today confirmed suitable, suppose is obvious as they supply the B and Q feed and expansion tank.
 
Status
Not open for further replies.

Reply to Expansion tank is it big enough. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

P
  • Question
Boiler is SIRIUS THREE FS 70 Potterton commercial. Situation: We are small building contractors and my labourers managed to damage the radiator...
Replies
2
Views
147
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
470
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
228
S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and...
Replies
2
Views
164
Sonya K
S
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
563
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock