Discuss UFH Motorised Valves? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
P

Paul Jones

Hi all - I have a UFH system in a fairly new house, problem is downstairs (zone 1 is fine) upstairs (zone 2) is cold - not getting up to temp, had a nose at the controls, pump etc and all seems to be ok except the honeywell motorised valve (HMV), when I move the pin to Manual the upstairs warms up in no time...two questions...

Is it just the HMV at fault?
Will it cause any damage by moving the MV to manual?

Hope you can help?:28:
 
Hi.
no it won't cause damage but check the stats are calling first. If they are then the valve is at fault. Do an electrical test and that will show it. Check the mixing valve is at 40-45 degrees and by overriding the valve that will get you going until you find what's at fault!
C
 
the controls sequence should normally go spur-clock-stat-valve- boiler+ pump. If you feel confident in testing electrics then you can logically test for the fault, if not then get a qualified heating engineer who understands controls to take a look.
 
the controls sequence should normally go spur-clock-stat-valve- boiler+ pump. If you feel confident in testing electrics then you can logically test for the fault, if not then get a qualified heating engineer who understands controls to take a look.

Is it much of a job to replace the HMV?
 
post a picture of the valve.

could meam a drain down of part or all the heating system.
 
Thanks for your replies - I am struggling to get a plumber to come and have a look - will try again tomorrow.
 
what area are you from? there may be a member on the forum who lives close to you.
 
Status
Not open for further replies.

Reply to UFH Motorised Valves? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

bit of an odd one. UFH been working fine for about a year or two now. today the pipes going to it before the zone valve are stone cold. its a...
Replies
2
Views
478
Hi I have a 4 zone / 7 loop UFH system. 2 zones (4 loops) always get hot when the system is on when the zone thermostats and actuators are...
Replies
14
Views
1K
  • Question
Hi guys, I have a set up with rads upstairs and UFH downstairs. I have installed the manifold for the UFH along with 2x Honeywell 2port values...
Replies
16
Views
2K
Do people with this type of mixed flow temperature control have any problems with achieving the required manifold flow temperature? The one below...
Replies
3
Views
730
  • Question
Have a sytem boiler with unvented cylinder with 2 heating zones plus hot water in a house we moved into recently. To start with we were always...