Discuss How bad is this system? in the USA area at PlumbersForums.net

Messages
24
Generally works okay, but bubbling when on hot water only. How can I easily alter this to works better?
Please see picture


Screenshot_20210809-203226_Gallery.jpg
 
Old gravity set up either needs moving eg feed and vent or as above sealing
 
Very bad. Someone has reversed the flow to allow a quasi-S-plan system but that means the cylinder coil flow and return are reversed, the cold feed and vent are reversed, and (could be a serious safety issue) the open vent isn't really open. Needs a competent plumber to modify that into a proper S plan.
 
Thanks for your replies, what about this set up in the picture? Or would it be a waste of time. The pump and valves are right next to the boiler,
so would be really difficult to get the vent and feed before the pump
20210810_104101.jpg
 
That's no safer mate. The vent needs to be off the boiler flow and before the pump ideally you will position the cold fill there as well with the vent first and the cold fill after with a maximum of 150mm between the two centres of the tee's.
 
Like this right one eg c
 

Attachments

  • B25E118A-57B4-459E-9E38-1E1065FB7384.jpeg
    B25E118A-57B4-459E-9E38-1E1065FB7384.jpeg
    52 KB · Views: 11
What boiler do you have? What systems are safe and possible depend on the nature of the boiler itself and its inbuilt safety features.
 
I would not install the pump and expansion vessel as shown in the image though. The plumber if he/she understands it will know where to position.
 
Okay , I showed him the diagram and he already said about putting vessel on the return side

Yes for a number of reasons, perhaps most the function and durability of the system is that the vessel should be on the return and with the pump shortly after, this way you will create a positive pressure through the boiler and throughout the system where it meets the vessel connection and point of no pressure change. This will ensure no air is drawn into the system, as well as not allowing any dissolved gases from being drawn from the fluid. Positioning the vessel on the return will also prolong the life of the vessel diaphragm as its not subjected to the higher temperatures.
Whilst the engineer is making the adjustments I would strongly advise a filter installed on the return as well and pay attention to the quality of water when draining down. Your system may benefit from a flush with chemicals.
 

Reply to How bad is this system? in the USA area at PlumbersForums.net

Similar plumbing topics

Can anyone remember the Mira mixer shower that would work down to a really low pressure on a vented hot water system without a shower pump?
Replies
2
Views
180
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
230
Hi, My current hot water system needs to be replaced. Anyone got any suggestions or can recommend any plumbers around Derrimut area that won't...
Replies
6
Views
360
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
286
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
563
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock