Hi Guys.

I'm having a consistent Airlock problem with 1 Radiator Feed Pipe, causing 1 Rad not to get hot. It happens about every 10 days or so, until i push it out by turning all other rads off apart from 1 which doesn't get hot. I hear a gurgle and then it pushes water through. I then bleed this rad afterwards and it is perfect for the next 10 days or so until cycle starts again...

It is a downstairs utility room radiator which is fed from the ceiling above it, it is only the 1 pipe which seems to have the problem, it is the only pipe not hot and i'm not really getting much air out anywhere else when bleeding, which makes me think it is a problem local to this pipe only.

I have had the floor up in room above it, and from what i can see the pipe branches from main heating feed and seems to go slightly uphill until it turns 90 degrees and goes down the wall. Could this be the issue the fact that it runs slightly uphill?

Thanks in advance,

Steve.
 
A slight rise in a heating pumped pipe (even if going to a drop) usually won’t cause much problems, except sometimes when draining and refilling a system.
You should also look at system to see if any way air is being absorbed, or if corrosion gases are the cause.
I discovered on a microbore piped system that was constantly every few months having a pipe to one rad air locking, that when I replaced the circulating pump (used a 6m pump) never again had the air lock.
Worth checking your pump is fully functioning, not blocked at impeller and set correctly.
 
A slight rise in a heating pumped pipe (even if going to a drop) usually won’t cause much problems, except sometimes when draining and refilling a system.
You should also look at system to see if any way air is being absorbed, or if corrosion gases are the cause.
I discovered on a microbore piped system that was constantly every few months having a pipe to one rad air locking, that when I replaced the circulating pump (used a 6m pump) never again had the air lock.
Worth checking your pump is fully functioning, not blocked at impeller and set correctly.

Thanks for the reply, it is a 2 Year old Baxi Megaflo. The pump is in the Boiler i believe, can this be set differently? (Apologies for basic question but i am only a DIY'er!)

Can corrosion cause enough air in system in a 10 day period?
 

Reply to Constant Airlock in 1 feed pipe in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
478
Afternoon. I have an issue with no water flow from any of the hot taps in the house, I can't seem to find a solution to the issue. System is a...
Replies
11
Views
368
We have a utility room with a washing machine but no sink. Wife wants sink. There is room to fit one and the waste will connect to wahing machine...
Replies
22
Views
563
Hi all, Got a nightmare situation with a central heating system I recently adopted. It's an open vent system with a combined F&E pipe, with a...
Replies
17
Views
2K
I have a badly blocked feed pipe to kitchen rad, was running very slowly but I’ve made it much worse trying to clear blockage with curtain wire...
Replies
6
Views
566
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock