Users can remove all display ads (not sponsors) for a small fee. Click for info (must be logged in)

Discuss Worcester combi boiler cutting out on hot in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Piperdave22

Gas Engineer
Messages
61
Replaced a bath tap with shower attachment and Fitted a Aqualisa Midas thermostatic bath /shower mixer . During the shower sometimes the water goes cold for a few seconds and goes warm again and customer said the boiler is cutting out then coming back on when it does this .
Almost like it’s reaching temp ,cutting out then firing back up

What could be causing this and what can I do to remedy it ? It’s a Worcester combi
 
The symptoms are typical of a blocked plate heat exchanger. Was the hot water running fine before you changed the tap?

If the new shower has a greater flow rate than the previous, it may just be highlighting an existing fault
 
Yeah all the others taps seem to be running at a decent pressure .
They were having a similar problem before where they couldn’t get the right mix on the shower and it would drop out the same but all other taps seem ok .
 
I got him to run the basin taps today to make sure it was everywhere doing it and whilst on the phone he said it was running then went cold and got hot again so tells me it’s definately a boiler fault
Only weird thing is he said if the heating is on the doesn’t last as long before getting cold
But if it isn’t on it lasts a bit longer
Have said it’s mostly likely to be a blocked heatplate but could be dhw thermistor or a divertor issue .
Boiler is only 18months old though so I’m hedging my bets towards a scaled up heat plate atm

Any thoughts ??
 

Reply to Worcester combi boiler cutting out on hot in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Recently had a Viessmann Vitodens combi boiler installed, quite often when the adjacent cold mixer tap is opened the boiler starts for a few...
Replies
3
Views
229
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer...
Replies
4
Views
281
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
204
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock