Discuss Which way round should the filling loop be fitted? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
What a mess, I have the same filling loop as diamond gas , the valve in this one as well, following the directional arrows will be fitted on the heating side, not big problem the valve can be easily reversed and fitted on the water main , my concern is the little Iso valve, it may had to fitted with the arrow pointing out of the CH side, any opinion?
 
Check valve is always fitted to the cold main side. If MI state different then you need to also comply with the water regs so need to fit an additional double check on the cold main. So it will cost your more if you follow MI in this instance.

Some chemicals can be dosed via the filling loop so having the check on the heating side wont protect the cold from contamination.

Happy birthday Bod :)


Cheers aw
 
BORING, I thought this question was done to death a few months ago :-/
Sorry to bore you mountain man, but I did try and look back over old posts before I placed mine. Unfortunately I couldn't find the answer I was looking for. Guess what, despite all the replies I have had so far, I still can't decide which way the loop should be fitted.
If the check valve fails in any position there will be a risk of contamination, don't forget some loops only have 1 iso valve attached to the check valve, so much for water regs then.
 
Sorry to bore you mountain man, but I did try and look back over old posts before I placed mine. Unfortunately I couldn't find the answer I was looking for. Guess what, despite all the replies I have had so far, I still can't decide which way the loop should be fitted.
If the check valve fails in any position there will be a risk of contamination, don't forget some loops only have 1 iso valve attached to the check valve, so much for water regs then.

Exactly why the subject is boring, too many conflicting replies to be of any help.
Traditionally there is one iso and one check valve with a flexible loop.
The loop should only be connected whilst filling the system then removed.
No chance of cross contamination then.
 
Sorry to bore you mountain man, but I did try and look back over old posts before I placed mine. Unfortunately I couldn't find the answer I was looking for. Guess what, despite all the replies I have had so far, I still can't decide which way the loop should be fitted.
If the check valve fails in any position there will be a risk of contamination, don't forget some loops only have 1 iso valve attached to the check valve, so much for water regs then.

My take in this is that the check valve is to protect the mains water and therefore any water leaving the mains to enter the heating must first travel through the 'protection barier' formed by the check valve! That way there's no way contamination can get back through except if the valve fails!

That's probably been said already, but there ya go :)
 
BORING, I thought this question was done to death a few months ago :-/

It is wrong to assume that all members have the time or patience to trawl prior posts in search of an answer. Occasionally topics can be difficult to locate depending on search tags, and don’t forget when you are under pressure you may need a quick answer. Even you are guilty of your perceived monotony. I note you requested help recently on an area which was addressed in 2010 (here are the links). A little searching around the forum may have helped? We are not all experts in all areas which is the reason we come on here; to learn and impart knowledge on others.
http://www.ukplumbersforums.co.uk/central-heating-forum/36710-ideal-isar-noisy.html

http://www.ukplumbersforums.co.uk/central-heating-forum/13456-ideal-isar-he-24-banging.html
 
It is wrong to assume that all members have the time or patience to trawl prior posts in search of an answer. Occasionally topics can be difficult to locate depending on search tags, and don’t forget when you are under pressure you may need a quick answer. Even you are guilty of your perceived monotony. I note you requested help recently on an area which was addressed in 2010 (here are the links). A little searching around the forum may have helped? We are not all experts in all areas which is the reason we come on here; to learn and impart knowledge on others.
http://www.ukplumbersforums.co.uk/central-heating-forum/36710-ideal-isar-noisy.html

http://www.ukplumbersforums.co.uk/central-heating-forum/13456-ideal-isar-he-24-banging.html

Point taken but an appliance specific question is not the same as one on a generic subject that had been 'done to death' a few weeks ago.
Besides, if the filling loop is bought in a plumbing shop then the staff there or another customer should be able to answer the question of orientation in a few moments.
 
I'm guilty of fitting them on the heating in the past mainly because the cheaper ones came without an iso and ignorance to be honest! I assumed the check valve had to go onto the heating side because of the directional arrow of flow printed on them. They must go as Chris has said ... On the cold water main :)
aggree the cheap ones can only be fitted that way been using the pts ones they have 2 valves
 
Status
Not open for further replies.

Reply to Which way round should the filling loop be fitted? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

If you are qualified to do a Gas Safety check on a property I assume that entails checking the boiler. If, when checking a Combi, you notice the...
Replies
9
Views
316
On my Valliant eco tec boiler the pressure guage is on red when cold . I drain a radiator to correct to pressure and it works fine and stays in...
Replies
5
Views
544
Oliver1234
O
Hi, Short version: I have about 4" of pipe sticking out of a concrete floor in a cupboard. It makes a 45-degree bend as it exists (bent, not with...