Users can remove all display ads (not sponsors) for a small fee. Click for info (must be logged in)

Discuss Wet underfloor heating system in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
M

MARIE1

My underfloor heating is set at 21 on the stat but the floor area feels cold to touch. I was expecting to feel a little warmth from it. I have since discovered that my builder has laid a 30sqm pack over a 50sqm area. Is this as bad as it sounds? Thanks in advance
 
Unfortunately - Yes.
Were there any heatload calculations done?

Do you have any photos of the piping at the time of installation?
 
Sounds like an expensive error you can either get it redone or pursue "builder" to try and get some money off. Begs the question why they didn't use an experienced plumber. See so many poorly installed ufhs by builders who think it's just a case of throwing it in
 
There's no such thing as a 30m2 pack... As ... It all depends upon the heat loss of the room, the designed flow temperature, and possibly the heat source.

Ask him for the heat loss calculations.

Old leaky buildings like the one I surveyed today, 150W/m2 house size 80m2 heat load 12kW
Then there's the new build we're working on 450m2 , 26W/m2 Heat load 12kW

The design and installations are completely different... (the first isn't suitable for ufh, the second we have to cool the house in the summer...)

What length of pipe did he install, how many loops, serpentine or snail,

What was the designed flow temperature for the underfloor heating?
Has he connected the flow and return the wrong way round?
Is the TMV on the manifold configured correctly?
Does the underfloor heating have it's own circulation pump?
Did he just tap off the existing heating circuits?
Are there in screed stats or just air stats?
 
Its a pity there arent more like worcester out there, too many doing things they dont understand! ps I dont touch ufh, as I know fa bout it :)
 
Status
Not open for further replies.

Reply to Wet underfloor heating system in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m...
Replies
6
Views
304
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16...
Replies
0
Views
228
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
425
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock