Had 2 interesting jobs this week on Heatslaves.

Firstly, fuse kept blowing (3.15A fast blows - always keep some in the van). Worked it down to the coil. This is the second Heatslave this month with the same diagnosis, anyone else had that?

Second job of interest was another HS with a leaking flow switch and burner lock out. I fixed the switch but couldntu get the burner to stay on. I tried the old trick of a quick off/ on just before lock out which fired her up but only until next cycle. This sometimes allows any damp in the electrics to dry out.
Then I found even more wet in the control box and base.
Turns out the flow switch was letting water through itself into the cable sleeve, up the sleeve to the 2 pin plug, dripping off the plug onto the base of the electrical housing right next to the burner umbilical. Water then draining down into the control box base!! I blew it through and loads came out.

So I added a rubber washer and some ptfe to the flow switch and cut the cable sleeving to let any water drain out until I get a new switch. I then dried the electrics out with a hair drier.

Annoyingly, I had a text this morning to say its blown the fuse again so something must be damaged. Lord knows how Im going to get to the bottom of that as the fuse is blowing so late on. I tested all the functions before I left so its nothing obvious.
 
Is this on the same boiler or two different ones?If so which one is still faulting?
 
Not had a fastblow with the coil. Normally pump or 3 port. At least its plug and play.

With the flow switch ive seen that a couple of times. I strip back the sleeve now so it stays outside the panel.
 
Is this on the same boiler or two different ones?If so which one is still faulting?

Separate boilers, leaky one still tripping. The drip from the flow switch plug did also get to the pump but could that blow intermittently?

Only other way is to keep going back and unplugging bits again but leave boiler 'on'
 
Check the stat in the control panel I have had the same problem when the water tracks up the cable sleeve from the flow switch it goes onto the stat and shorts it out
 
Found the latest problem, water was tracking up one of the the actual wires aswell as the sleeving on the flow switch but also the diverter valve was leaking into the pump. This thing will end up like Triggers broom....
 
Status
Not open for further replies.

Reply to WB HS - electrical issues in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and pebbles!) We saw that the pipe that takes water down the gutter was visibly full to the top. He said he will return with a coil to push through...
Replies
1
Views
65
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Hi bit of a weird issue, I installed a grohe bathroom tap successfully 2 months ago bought from screwfix. Last week the right hand hot tap makes a squeak noise as I turn it on or off, left tap is 100% perfect and noiseless. This grohe tap is like one unit, so no screw notch or way I can remove...
Replies
3
Views
140
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
231
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock