That "upper operational limit is only the pump end of curve conditions so as the pump is new it does point to a restriction in the Hx or else the loops are full of sludge. You may have to prove both clear .
 
That "upper operational limit is only the pump end of curve conditions so as the pump is new it does point to a restriction in the Hx or else the loops are full of sludge. You may have to prove both clear .
No way to increase flow really as pump speed is controlled by boiler and all loops are fully open. Viessmann tech suspects calcified main heat exchanger due to limescale buildup but theory doesn't explain boiler noise nor still fluctuating tap temp with brand new plate heat exchanger.

I'm leaning toward these pieces of magnetite floating around the circuits causing blockages.
There was black oxide in the old plate heat exchanger so that was cleaned out once but possibly coming from boiler parts corrosion as we have no rads? Thinking to install a Magnaclean or Fernox TF1 or equivalent on the return hopefully it picks up whatever is lying around.
 
If you are handy yourself, maybe connect mains hose to UFH manifold with return disconnected, you will then get a feel for head required to give a flow rate of 1LPM/Loop by cracking open the mains.
You said originally no problems with DHW on old Hx but now some problems with new HX?
 
If you are handy yourself, maybe connect mains hose to UFH manifold with return disconnected, you will then get a feel for head required to give a flow rate of 1LPM/Loop by cracking open the mains.
You said originally no problems with DHW on old Hx but now some problems with new HX?

Will try.
New circulation pump inside the Vitodens had zero improvement or aggravation of the symptoms. Same low flow rate, same short cycling overshooting of heating temp on lower settings and sometimes luke warm/hot at the DHW taps/shower. Funny metallic gurgling noise from back of pump (both old and now) when boiler is heating but when also idle with pump operational.

Thinking hoses are flaking and constantly obstructing the plate HE, main HE and pump. Possibly in the UFH loops as well.
 
@John.g - I aired every UFH loop via tap mains pressure and it was ridiculous how low of a head pressure was required for 1L/m! At full blast the gauges were flat down at 4L/min. So it's definitely a circulation problem. Although some of the loops had quite a bit of air in them, even after the slighty tedious work to refill them all and air them one by one, the problem is the same and the boiler behaves identical. Maybe the floor heating has better coverage and more even heating. Definitely a circulation issue, likely boiler side as no blockages in the UFH.

Any ideas what I should do at this point?

  • find yet another Viessmann service partner to come and look and pay the call out fee to get an additional opinion
  • agree to replace the heat exchanger and hoses €1200+... and pray it's the actual problem as "no return policy on the HX" and if that doesn't work...
  • buy a new boiler + install @ at least double the cost of the HX replacement, try to sell the old one for parts to make up some of the $ spent on the part replacement.

What worries me about the heat exchanger suggestion is the strange bubbling noise behind the pump, maybe due to the alleged blocked heat exchanger some water is flowing backward or bubbles somehow making this noise? I'm worried it could also be something with the AquaBloc which is all one big (expensive as usual) piece on the Viessmann which causes some obstruction or problem with circulation.
 
Maybe try and figure something out from the DHW (combi?) side, set the boiler HW setting to 3 or4? then open a hot tap fully or even two, measure these flow rate(s) and measure the DHW temp, see if you can can read off the boiler flow&return temps or just the flow temp if only one available, may be able to figure/confirm something from these readings.
 
Maybe try and figure something out from the DHW (combi?) side, set the boiler HW setting to 3 or4? then open a hot tap fully or even two, measure these flow rate(s) and measure the DHW temp, see if you can can read off the boiler flow&return temps or just the flow temp if only one available, may be able to figure/confirm something from these readings.

DHW Rotary Knob Setting: 4
Hot water tap on full: 10.25L/min
Hot water temp: 40C
Boiler temp: 65-80C

Heating Rotary Knob Setting: Between 4 & 5
Heating flow: 47C
Heating return: 27.5C
Boiler temp: 49-50C
Manifold flow meters: ~1L/min flow meters open fully - all thermostats on, 9 loops.

After turning off the hot water, if I put one hand on the top of the heating flow pipe coming from the boiler and the second hand 1 meter lower, I can feel that the heated water comes through very slowly.

Attached is a recording of the strange noise behind the circulation pump inside the boiler coming somewhere from the Aquablock, behind the pump.
-no water leak or any air from airvent nor the pressure release valve
-system and boiler were recently vented.
-pump is a Grundfos UPM3 15-75. Replaced recently as was the suspect problem, however boiler behavior and noise same as with original 4 year old pump.
-noise reduces in intensity but does not go away after a few moments when pump circulating at lower power in central heating mode.
 

Attachments

  • New Recording 3.mp4
    154.2 KB
It does sound dodgy the only way to find out is strip it out which will need a engineer with a spare pump , as I've said before in my opinion you need a external pump on the heating manifold to push the heating water through the heating loops and back to the boiler , you haven't posted any pictures of your system as requested so we're all stabbing in the dark really.
 
Certainly sounds like a bag of nails and metallic like noise.

From DHW tests the boiler output was 21.5kw (assuming 10c mains) difficult to say what the primary flowrate was but would estimate ~ 10 LPM, what is a bit strange is the variation in boiler temperature, 65C/80C, I would have thought that the boiler would just modulate down to maintain that 21.5kw, did you notice if the boiler ran continuously during this test or was it cycling?, if so then one would expect DHW temp fluctuations as well.
Maybe just repeat this test sometime with DHW setting to max, I would expect the boiler to run continuously as the DHW heating demand is then ~ 36kw, don't know what your boiler output is.

From heating tests the boiler output was 13.8kw at a flowrate of 9LPM.
 
@king of pipes Here are the photos of the installation. I am aware it is quite a hack job - not done clean and well. Looking back I should have done more research on the installer and asked why no mixer valve, external circulation pump, pressure and temp gauges were installed, which inhibitor or water treatment they used for the fill and asked to do a neat organization of cables and floor. At least I know more now about it for the next project... Live and learn :)

RE: external pump... what i'm wondering is why it worked 'well' for 4-5 years with decent flow rates, no short cycling, ok steady temperature control
 

Attachments

  • IMG_7550.jpg
    IMG_7550.jpg
    333.2 KB · Views: 28
  • IMG_7551.jpg
    IMG_7551.jpg
    158.4 KB · Views: 28
I can't answer that but what I can say is if you look at my first ever post answering you there a picture of how it should be done ? , a small low loss header with a separate pump fitted would also do the job on your existing set up look at the Viessmann installation guide it may give you a better understanding . Kop
 
Is that the system with the manifold circ pump and where you run the boiler at say 60/65C and UFH at 35/35C which reduces the primary flow rate substantially?. Your post #23.
 
I can't answer that but what I can say is if you look at my first ever post answering you there a picture of how it should be done ? , a small low loss header with a separate pump fitted would also do the job on your existing set up look at the Viessmann installation guide it may give you a better understanding . Kop
Totally agree
 
If the pump speed is limited to 72% then the 7.5M pump becomes < 4M which probably isn't enough for 12mm piping but strange that the system worked OK apparently for years.
 
I can't answer that but what I can say is if you look at my first ever post answering you there a picture of how it should be done ? , a small low loss header with a separate pump fitted would also do the job on your existing set up look at the Viessmann installation guide it may give you a better understanding . Kop

@king of pipes - wholeheartedly agree. After all the research and help from this forum I know much better of what a proper UFH should look like.
The OEM circulation pump inside the boiler is the Grundfos UPM3 15-75 which also comes as a UFH pump. If I were to add another pump to the system, wouldn't it basically be running two pumps? Is it because of the thickness of pipes that so much pumping pressure would be needed? If we had say 10 rads in the flat instead, would an external pump not be necessary then because of larger pipes? We are on a one level 120m2 with 16mm PERT-AL pipes.

Is that the system with the manifold circ pump and where you run the boiler at say 60/65C and UFH at 35/35C which reduces the primary flow rate substantially?. Your post #23.

@John.g - are you referring to @king of pipes ' setup?

If the pump speed is limited to 72% then the 7.5M pump becomes < 4M which probably isn't enough for 12mm piping but strange that the system worked OK apparently for years.

Piping is 16mm. 120m2.
Agree it's strange that it worked but I'm not so sure the manifold area is the problem since the noise behind the pump and possible circulation seem to be an issue also when just DHW is being used (if I turn off central heating).
 
Last edited:
Well, I would be quite surprised if one pump couldn't give adequate flow through 16mm piping, my daughter has a mixture of rads/UFH serviced with a 16 year old Grundfos selectric 6M (one) pump, all heating working perfectly.

Don't know what length the loops are but assuming 100M then the pressure drop through each loop is 0.152M @ 1LPM, 0.54M @ 2LPM and 0.82M at 2.5LPM, these numbers become 0.18M, 0.66M & 1.0M for 120M loops.

I know you are in a dilemma after spending all that money but if I were you (and should have suggested this previously) I would go away and buy a 0 to 10M pressure gauge, install it in the UFH flow side of the manifold and run your system, that will tell a lot and may save you a pile of money at the end of the day. Also find out if that circ pump is restricted to 72% speed.

Yes, I was referring to KOPs post/photo.
 
Well, I would be quite surprised if one pump couldn't give adequate flow through 16mm piping, my daughter has a mixture of rads/UFH serviced with a 16 year old Grundfos selectric 6M (one) pump, all heating working perfectly.

Don't know what length the loops are but assuming 100M then the pressure drop through each loop is 0.152M @ 1LPM, 0.54M @ 2LPM and 0.82M at 2.5LPM, these numbers become 0.18M, 0.66M & 1.0M for 120M loops.

I know you are in a dilemma after spending all that money but if I were you (and should have suggested this previously) I would go away and buy a 0 to 10M pressure gauge, install it in the UFH flow side of the manifold and run your system, that will tell a lot and may save you a pile of money at the end of the day. Also find out if that circ pump is restricted to 72% speed.

Yes, I was referring to KOPs post/photo.

Thanks.. I would assume also loops are less than 100M since some of the larger 20-40m2 rooms were split into 2 or 3 loops but I don't have the schematics used during construction. Circulation pump is at 80% speed.
 
Didn't use proper wall thickness for that 16mm piping so I think a ID of 12mm so the corrected numbers for 100M loops are 0.32M @ 1LPM, 1.16M @ 2LPM & 1.75M @ 2.5LPM so the boiler circ pump running at 80% should still give a flow rate > 2LPM.
 
I've seen far worse installations. In this case no mixing valve is required since the boiler is itself supplying the water at the required low temperature. Short pipe runs to the manifold mean not too much loss of head. If it used to work, then the basic design may not be at fault.

If the OP isn't getting more than 1 lpm even with only one circuit open, there is very obviously something wrong. The fact that water is flowing at all would seem to rule out airlocks in the UFH pipework, but there may be some kind of algal blockage that has developed over the summer season. Nothing to stop the OP isolating the UFH manifold from the boiler and mains flushing a circuit using a hose to see what the water is like and if there is any blockage.

EDIT If number of circuits open does not appear to affect the flow through the circuits that are open then pump would appear to be on a constant pressure setting.
 
Last edited:
Have you ever noticed/noted the manifold pressure (if PG installed) on a UFH system without a manifold pump.
If that's a question for me, then afraid the answer is no, but it would be very useful information if someone here has it.

Thinking about it, it's not uncommon to see a 2kW radiator run on a 10m or more run of 15mm copper tube which has similar internal bore to 16mm MLCP UFH pipe and this could be achieved at a fairly low head. A UFH circuit may be much longer, but won't be 2kW. So there oughtn't be a lack of pressure to drive at least one circuit (...unless the pump ports/boiler H Ex etc. are obstructed) or the UFH circuits are themselves obstructed.

If an inline flow gauge is an option, what if the OP were to create a short circuit by attaching a braided hose across the two hose connectors at the end of manifold? If a decent flow were then obtained, that would point to the issue being in the UFH circuits themselves rather than in the boiler itself?
 
His low flow rate may be partly be because the "Maximum speed setting in the delivered condition" for the boiler is 80% so this makes it a 4.5M pump, don't know if this setting can just be changed to the 100% rating of 6.8M which the previous pump may have been set to?. It also mentions residual head, not sure if this means the head available after allowing for the Hx. Setting may be changeable from the boiler menu??.


1639670992023.png
 
Hi John,

To probably slightly mis-quote "The Lion the Witch and the Wardrobe", the OP states the system worked correctly for 4 years and so either he is lying, or he is telling the truth, or he is mad (or mistaken).

I think we need to work on the assumption that the OP's statement that the system has worked for 4 years is correct as otherwise this is a waste of everyone's time. I don't see why we are trying to prove the technical feasibility of a no external pump setup when 4 years of working order has already done this. My own UFH manifold at my own home tees off the primary flow in 15mm which is wrong by every rule of thumb and I had to defend the decision on technical grounds when discussing with colleagues until after I'd installed it, after which, the fact that it functioned perfectly made such defence of my 'undersized' pipework unnecessary.

While it may be interesting to explain why the OP's system should work, if it cannot be made to work, then some of the others may be right to say such a single-pump system can't work, but that implies that the OP is not correct to say it formerly did work. We cannot all be correct.

Looking at your chart, we can have up to 5.5lpm total before we fall below a 4 metre head, and if the circuits will have enough pressure on a 3m head (minus resistance of primaries and boiler itself) to run properly, then we have 13lpm available flow which should give each circuit about 1.5lpm which ought to be enough really. The problem is we don't know if a 3m head is available at the circuits, but an undersized pump would be indicated by dropping off of flow to each individual circuit as more and more circuits are opened. Looking at the data for the UPM3(K) AUTO XX-50 130/180 (N) which is, I think, the kind of pump that might be fitted to a UFH system, its highest constant pressure setting is only 3m anyway, so unless the boiler/primaries in the OP's case are robbing more than 1.5m head, he should have at least enough oomph to run 2 circuits at 1.5lpm with the pump you have shown the curves for.

At this point, we need to wait to hear back from the OP. From that funny noise in the boiler, I'm thinking the UFH circuits are not at fault and something is up with the boiler (which was the original assumption) but it would be nice to rule out the UFH, and it might be something really silly like someone had fiddled with the flow adjusters on the manifold, or an isolator valve is remaining partly shut although it looks open.

What about this kind of approach?:

How might the OP prove the manifold is at fault? I think your idea of testing the flow at a specific working head is good, but may be a job for a plumber rather than a DIY one, though I suppose we could guide the OP through the process.

How might the OP prove the boiler is at fault? It would be very easy to fit a low loss header and then find, if the boiler is at fault, this has 'cured' the flow issue through the manifold, but things still wouldn't work properly and it would probably reduce the boiler efficiency as well as be an expensive experiment.
 
The cheapest way to see what the actual head is, is to install a PG which the OP I would think is capable of doing since he flushed out the manifold, the other approach is to ask Viessmann if the circ pump can be set to 100% because I don't think anyone would be happy to run a UFH with a single 4.5M pump which this pump effectively is at 80% speed. The original pump may well have been set to 100% which would go a long way to explaining normal performance for a few years.
 
He could quite easily install a pressure gauge on the 3/4" BSP hose connector isolators. It would presumably show differential pressure relative to atmospheric so he'd need to subtract the system charge pressure from the pressure created by the pump in action, but it would give an idea.

Does the following sound right? If the assumed blockage is between the return rail and the pump inlet on the return side, you'd see a good pressure measured at the flow rail and at the return rail. If the blockage is the UFH circuits themselves (which might just be acting normally due to their inherent resistance), you'd see a lower pressure on the return rail than on the flow rail, and if there is not a decent pressure on either rail then the blockage is between the pump outlet and the flow rail, or the pump is not running properly for some reason.

If that's your plan, I think it's an excellent way of locating the problem and will help even if the problem proves to be internal to the boiler.
 
Yes, you are correct, he would really need 2 PGs, one on the flow, the other on the return, for some reason or other I thought it was a OV system so the PGs would need to be 0 to 3bar which makes it difficult to get a accurate differential reading of say 0.2bar between the two but worth trying at any rate?.
 
OP here. Thanks for all the idea brainstorm.

I've isolated the manifold and flushed every loop for 5' with tap mains. Water is clear. No blockage. Bit of air in some loops but not much. Flow rates way over 4LPM (max of the gauges). I don't think there is a blockage in the manifold itself because as previously mentioned, even with one circuit open, flow rate is max 1.5LPM. If the boiler was fine but the manifold or UFH was the issue then hot water would be running perfect when CH is off however the boiler runs hot... 75-85C at times as it modulates up and down.

Viessmann & the tech's current theory is blocked main HX (calcified). Pump cannot get enough pressure through the main heat exchanger to move the water around. The sound possibly has something to do with it. Pump is brand new (few weeks old). This theory might be plausible although not sure if it explains the sound from the hydroblock. However Viessmann tech has done a 2h power wash with acid (don't ask me which) to remove limescale in the HX, didn't change anything in terms of boiler behavior or noise. There's nothing else behind there besides the PRV and automatic air vent. Could it be some back-flow into the pump due to the alleged 'blockage' in the HX?

Another strange thing, we do not have an outside temperature sensor and weather dependent mode on (installer couldn't get access to drill on a proper outdoor place or some reason like that) and the manual says without wether dependent mode, pump speed can't be changed, however I seem to be able to still do it. I can change the speed up to 100%. At 100% it just makes more noise like a car engine on high revs, but LPM flow doesn't change!

I'm going to look into finding some pressure gauges and fit them at the fill/drain connections of the manifold.

@Ric2013 I might qualify for the mad/mistaken part but if my memory serves me right, this noise never existed in previous years, boiler was running at low temps in CH without issues at 35-45C flow and flow meters were showing more than 2LPM so something went bonkers this year. All flow meters are fully open during this troubleshooting.
 

Attachments

  • Screen Shot 2021-12-17 at 01.41.08.png
    Screen Shot 2021-12-17 at 01.41.08.png
    89.9 KB · Views: 16
  • Screen Shot 2021-12-17 at 01.41.17.png
    Screen Shot 2021-12-17 at 01.41.17.png
    89.2 KB · Views: 19
Why should the main Hx be calcified, its a closed system and except there is a constant leak somewhere and the system is being topped up with a auto fill PRV. If the system is manually topped once/twice/annum and the filling valve(s) are then shut then calcified Hx should not be a problem. Was this Hx ever changed?. Can understand if it was the DHW Hx was getting calcified due to constant mains water through one side of it.

One simple test you can do is to carefully note the boiler pressure before fire up and circ pump start up, as soon as the pump starts up, again carefully note the boiler pressure, if the E.vessel is teed in before the pump suction then the pressure should rise by the pump head, if teed in after the pump then the pressure may fall by the pump head.

Another manifold test which may be worth doing is to disconnect the flow and return, get one 0 to 1bar PG and install it in the flow side of the manifold or install it in the mains filling hose, then open the mains filling hose isolating valve slowly and note the pressure with flow through all the loops on together at say 1LPM/loop, 1.5LPM/loop, 2LPM/loop & 2.5LPM/loop. This should give a indication of the pump (differential) head required at these flow rates.
 
To many if buts and maybes going on here all the info the op needs is in the manufacturers instructions it's just a matter of studying them closely and putting it into practice, the boiler needs to be installed and configured to supply the correct amount of flow through the heat exchanger in my opinion it isn't .
 

Attachments

  • Screenshot_20211217-044103.png
    Screenshot_20211217-044103.png
    176.3 KB · Views: 17
  • Screenshot_20211217-044756.png
    Screenshot_20211217-044756.png
    140.8 KB · Views: 15
  • Screenshot_20211217-050408.png
    Screenshot_20211217-050408.png
    436.2 KB · Views: 13
  • Screenshot_20211217-044206.png
    Screenshot_20211217-044206.png
    311.6 KB · Views: 13
Can you send on a link please KOP to that manual or just the pressure loss through the HX.

The OP states that he has seen flow rates of 2LPM= 18LPM/9loops or a boiler flow rate of 1080 LPH. My calculations show a required head of 1.16M (@2LPM) assuming 100M/loop, allow another 25% for elbows etc then the required head is ~ 1.5M or allowing another 72% still results in a required head of "only" 2M.
You can tell from your manual, the pressure loss through the (clean) Hx. I don't know what this is but assuming that the total pump head required is 4.5M then in your opinion should the boiler supply this without any problem or not?, ie a flowrate of 1080LPH @ 4.5M or so?.

dr might inform of the output of his boiler, if not already done so.
 
Here you go John busy on breakdowns I don't think it will I could be wrong thinking it needs a low loss header ? Kop
 

Attachments

  • 1706 Vitodens 100-W B1HC B1KC Installation and Service Instructions.PDF
    13.9 MB · Views: 11
Why should the main Hx be calcified, its a closed system and except there is a constant leak somewhere and the system is being topped up with a auto fill PRV. If the system is manually topped once/twice/annum and the filling valve(s) are then shut then calcified Hx should not be a problem. Was this Hx ever changed?. Can understand if it was the DHW Hx was getting calcified due to constant mains water through one side of it.
Closed system. Annual top-ups. No previous flush of heating water. Unknown what original installer put in the water if anything. The UFH is 120m2 so with an average of 5m of pipe per m2 and 0.15-0.17L per m of piping I'm estimating around 90-100L of water in the UFH. Is that enough to calcify a main HX? It's the original one. Boiler was new and installed 5 years ago.
The plate heat exchanger was recently replaced. Looking back I don't think it needed to, a flush and some chemicals would have been enough. It didn't look too calcified.
dr might inform of the output of his boiler, if not already done so.

It's the 2017 100-W B1KA 24kw combi.

it needs a low loss header

I was under the impression these are more for commercial setups with multiple boilers providing separation from multiple circulating pumps. I think if they would have done the job properly or had I had more knowledge at the time, then an external circulating pump, mixing thermostatic valve, low loss header, pressure/temp gauges, a filter, all should have been fitted.
 

Reply to Viessmann Vitodens 100-w trouble maintaining central heating temp in the USA area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
221
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
316
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
226
Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic Pushfit seems to be getting better and better, cost and convenience was always better, but now the quality is to, have we reached a stage where plastic will...
Replies
2
Views
230
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...