Discuss Unvented heating system pressure in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Matthew Score

Gas Engineer
Messages
26
I have an issue with a Ideal logic 35kw boiler and system pressure.

Boiler was over pressuring and the prv kicked into action and released the excess pressure as it should.

My issue is I have changed the expansion vessel and prv.

Filled the system to 1.5 and set the heating running and at full temperature it went up to 3.

The system is quiet large, dormer bungalow with 12 x 600 x 1000 K2 rads.

Does the system need a second expansion vessel? Is the water volume to large for the one 10l internal vessel?

I have never had this issue before, just scratching my head a little bit.

Thank you for any advise given
 
Yes that often happens need to change that is a bit on the low side for expansion but you say it worked before , drop the system pressure to 1 bar see what happens ? Kop
 
You rang ?
 
You check the hose isn't blocked to the expansion vessel

Rule of thumb 1l per rad
 
Whats the crack for Matthew here

Mathew send us your gas safe number I will process the request while he's building his post count ;) past 10

Help away will sort the thread out after
 
I changed the pipe, it was a bastard to get it to re-seal as it's down the side of the pump and wouldn't engage properly and weeped.

In the block wasn't crudded up / blocked ?

Eg got water at expansion vessel
 
Would say vessel too small then defo
 
+1 for the vessel being too small. Basically, the internal vessel is there to protect the boiler itself and will also do a few rads on a small system. Good advice given in this thread.
 

Reply to Unvented heating system pressure in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem...
Replies
9
Views
403
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
509
losing pressure
L
Hi all not a plumber but am an engineer I have pressure drop in the system Worcester Bosch came back after repressureising the expansion vessel...
Replies
2
Views
510
hello we have an unvented system. we have an issue where the hot water is hot for 10 seconds and then luke warm, turn off taps / wait and turn...
Replies
5
Views
732
Can central heating / gas engineer expert help me with below issue. During winter time only, I have been having issue with low pressure or...
Replies
0
Views
611
Back
Top