Posting here as the unvented G3 forum does not let me post.
I am hoping someone could apply some logic and help me with a problem that two plumbers have not been able to diagnose properly.
Details :
Unvented system.
Incoming mains with prv set at 2 bar. Plumber has checked this at ktchen mains.
Cylinder has two immersions. I can hear both cut off and cpme on again so presumably no thermostat problem.
The cold water relief valve set to 3.5 bar is letting by ONLY when the immersion is on (either of them).
The G3 plumber who serviced in November found the expansion vessel pressure at 2.4 bar. He recharge to 3.5 because a sticker on it said 3.5 - presumably this is the pressure put in it in factory ?!
After he left, started letting by again - so next suspect was the valves.
I got other plumber to replace the erv and tp valves. Now still letting by cold water when immersion on. This plumber said it now can only be the incoming reducing valve that has failed.
To me both these are illogical.
Can someone explain why 3.5 bar is right pressure ? To me this is too high relative to the 2 bar incoming so that it is like not having an expansion vessel at all, so the ERV then opens.
Also if the main pressure reducing was faulty the valve would be letting by all the time because the whole system would then be above 3.5, cold or not.
I am at my wits' end because you pay good money and they seem to do the wrong thing and not be able to think through. The second plumber did not even have a pressure gauge wih him and did not say anything about the expansion vessel.
I now have new valves and am inclined to just reduce the expansion vessel pressure closer to 2 bar which i bet should solve it.
Any advice please ?
Many thanks
John
You have a 210 Litre Water Cylinder, if its heated to 60C, giving it 10C deviation up to 70C then the expansion at this temperature is 2.18% so your expansion vessel must accommodate 4.6 litres of water without lifting the relief valve.
Assuming a pre pressure of 2 bar (the correct one) and a mains pressure at 2 bar here are the final pressures for a few different sized E.vessels
15 Litre: 3.3 bar (too near the limit)
20 Litre: 2.9 bar.
25 Litre : 2.7 bar.
30 Litre: 2.5 bar.
You are happy that the mains pressure isn't creeping up and I assume that the hot water temperature isn't exceeding 60/70C?
As you are probably well aware its vital that the pre pressure is not greater than the mains pressure of 2 bar, when checking it make sure that there is no pressure on the water side.