whats the copper pipe on rhs of bottom manifold ?
It's the return to boiler. The chrome pipe above is a bypass.
It's a Wundafloor system by the looks of it.
The problem is very simple. Your motorised vslve is being held open manually.then your main pump can force water throght the loops.
Job need finishing,wiring up and testing. If you let the motorised vslve close msnuslly it will stop getting warm.
 
thats return by the looks

and i guess there is non return in the bottom right end of manifold to prevent pump drawing from the return
 
me neither, cant see the need for that chrome bypass pipe either.
 
thats return by the looks

and i guess there is non return in the bottom right end of manifold to prevent pump drawing from the return
On these, the non return is on the left hand side of the manifold. Just before the pump. The bypass works when the pump starts up an before the heads have opened.
 
I don't like it., but chalked has answered the OPs question in #23
 
Thank you Chalked. Yes it is a wundafloor and everything you have said about the bypass and boiler return and non return is correct.

I thought I would have been able to at least get hot water circulating through the manifold (even with the loops closed) at the boiler temperature with the motorized valve on manual and certainly no flow temperature drop when the circulating pump is switched on irrespective of whether any controls are wired.

There is a pump in built to the boiler as its a system one.
 
It's the return to boiler. The chrome pipe above is a bypass.
It's a Wundafloor system by the looks of it.
The problem is very simple. Your motorised vslve is being held open manually.then your main pump can force water throght the loops.
Job need finishing,wiring up and testing. If you let the motorised vslve close msnuslly it will stop getting warm.

Exactly what he said
Get it wired correctly and jobs good
 
Status
Not open for further replies.

Reply to Underfloor Heating Unexplained Temperature Drop in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I'm attending a wet underfloor heating system, it's an old one ..No flow meters, just adjustable valves on the returns with conventional...
Replies
3
Views
540
G
HI folks, is it possible/feasible/reasonable to insatll an ufh manifold and system (for a 17m2 room) from a disused CH 15mm flow and return? I...
Replies
2
Views
568
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem...
Replies
9
Views
401
As part of deep house renovation, planning to install wet ufh on the ground floor, and radiators on upper floor. Two bathrooms will have both...
Replies
0
Views
644
Hi All, Looking for a bit of advice on the best way to pipe this. - 24kW Worcester regular boiler in kitchen, approx. 9 years old - unvented...
Replies
16
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock