thekidda

Hi All

I currently have an s-plan central heating and hot water setup but I want to replace my old oil boiler with a wood pellet boiler. I gather from everything I have read that I should install a thermal store/accumulator tank for the wood boiler to burn efficiently but I don't know how this would fit into an s-plan layout. All diagrams I have seen that include an accumulator have no hot water cylinder and just have the hot water running through the accumulator, but I'd really like to keep my cylinder for various reasons.

Can I actually have a hot water cylinder as well as an accumulator? And would I have the hot water cylinder heated by the accumulator or directly from the boiler? My gut feeling is that I would have the boiler heating only the accumulator and then both the hot water cylinder and the radiators heated from the accumulator.

I have spoken to some heating engineers in the area but very few seem to know about installing accumulators. Those who do are expensive and want to charge just to come out and look at my current system. Obviously I'm happy to pay for the work but at the moment I just want to know roughly how it will fit together so I can budget for the job.

Thanks in advance
 
Yes you can still have a hot water cylinder with a wood pellet boiler it's piped exactly the same you put a buffer tank next to boiler and feed house from that
 
So would you then use the (hottest) buffer water to heat the HW cylinder on it's own timed and pumped circuit?
 
You use the hot water out of buffer tank to heat hot water coil and heating it's just done the same s plan but you draw out of buffer tank instead of boiler
The wood pellet boer just heats up the buffer tank
 
Gray is spot on I have just fitted a grant thermawave it has a wood burner on gravity to it and solar panels on it ,an oil boiler, the hot water from the store is then pumped to the indirect unvented cylinder and heating circuit with the oil boiler as a backup. Customer over the moon.
 
Hi All
Thanks for getting back about this query. In the year since I posted it I have done a lot of homework and spoke to a lot of people about it and eventually came up with the same solution you are discussing. The wood boiler will heat only the buffer tank and the rest of the CH & HW system will simply run off the buffer tank instead of the boiler. We have just finished installing the new pipework layout and as soon as the weather is warm enough to switch off the central heating we will rip out the old boiler and install the new one and the buffer tank. Well, that's assuming I can figure out how to get the 750kg new boiler down the narrow hill to the cellar at the back of my house, then get it through the door and into place - the problems never end.
Cheers
 
Just one tip make sure you get an electrician that understands the system and what he needs to do to make it work etc
 
Just read your post on this thread as I am about to carry out similar installation, solar and wood burner into accumulator with boiler as back up. Any chance you could advise how you configured system for oil boiler as back up, the existing boiler on site is a combi, with the heating split on 2 zones for underfloor and rads separately. Hope this makes sense ??
 
There are no hard and fast rules and the instructions that came with my thermal store were a bit vague. I had the wood burner running on gravity with the oil boiler linked in to the store as with the solar and also the unvented cylinder. A twin channel programmer for the CH and DHW and a single channel for the boiler. The store is on a thermostat so when it reaches 50degc ( might need a bit of adjusting) it is then able to distribute heat to wherever it is required otherwise it could cool the system down until the store catches up. When the store has made 50c and there is a call for heat on CH a two port valve opens (heating and hot water on S plan) which brings on the pump and circulates it. Now if there is not enough heat from either source then the single channel boiler will need to be brought on along with the twin chanel programmer and there we have it valve open to CH or DHW pump comes on and boiler comes on. This works quite well and there may be a bit of minor tweaking but the customer is well pleased. Solar side is different because of the solar controller which works on a temperature differential. Hope I have explained it ok.
Forgot to say a 2nd pump is required for boiler only.
 
Last edited by a moderator:
Hi,

You might want to take a look at the Grant Spira condensing wood pellet boiler, they don't need a buffer tank, I understand they have a network of trained installers in the UK.

The Manufacturer has had this boiler under developement for over five years before releasing it to the market unlike many of the E.U. manufacturers who sold wood pellet products in Ireland using the customers installation as the research lab.

That said if you prefer the idea of the buffer store instead of looking at very technical installations I suggest you use the following as a guide to your supplier / installer:

Wood pellet boiler answers only to the buffer tank:

Buffer tank answers only to the house:

The above means instead of your thermostats calling "On" the boiler they call "On" the pump on the buffer tank to satisfy the zone including the hot water cylinder.

We ended up literally dumping the majority of the manufacturers high tech control systems and making our own simple controller that calls the wood pellet boiler on using the temperature of the buffer tank.

I hope the above is of some help.
 
Hi peteheat,

As a brand new user of this forum I was happy to see your post above as it virtually encapsulates my thoughts on my planned installation.

I am planning to install an ATMOS wood pellet boiler with an accumulator (buffer) tank. I have done the heat load calcs for the house, which is a large-ish, 4 bedroom stone built detached place in the French countryside. Virtually no double glazing yet but comprehensive loft insulation. My house heating requirement works out at 14,894 W plus a DHW allowance of 2,000 W giving a total of 16,894 W.
There are only two of us but full time occupation of the house. I have not made any 'diversity' allowance for rooms which will not be always heated, but I figure a 15Kw unit may be sufficient, rather than an oversize 20Kw boiler.
The design calls for TRVs on all rads ( total 14 rads) and the piping will be in PER /PEX 22mm to 15mm to 10 mm as dictated by heat load at various points.
I imagine a 2000 litre heat store with the CH + DHW pumped from that and the pellet burner only firing to maintain the heat store.
Pellets will, ultimately, be fed from a bulk hopper after delivery by tanker.

As a 'newbie' on the forum I would appreciate all and any comments / suggestions / criticisms from anyone.
 
Hi welcom to the forum, I think a 2000l accumulator is too large for a 14Kw Wood boiler. You could go for a 800l accumulator in my opinion
 
Hi welcom to the forum, I think a 2000l accumulator is too large for a 14Kw Wood boiler. You could go for a 800l accumulator in my opinion

I agree far to big I'd be going between 500 to 800 no more
 
The comments are appreciated, but......What is the logic of 2000 being too big? I had assumed that the larger the store of hot water, the less firing time needed by the boiler, assuming of course that the temperature decay in the heat store can be minimised by substantial insulation.
 
no you've got that round the wrong way. the larger the amount of stored hot water the larger amount of energy needed to keep it at the required temperature notwithstanding the amount of insulation. 2000l is enough for 8 baths one after the other without waiting for the water to reheat imho.
 
Many thanks for comments, I realised I had worded my last post rather badly. I meant to say that I had assumed that a larger heat store would reduce the frequency of boiler firing rather than less firing time.

ecowarm, where does the 1:50 ratio come from? I don't doubt you are right but am curious thats all.

If I go for an 800 L store that will be a bonus on cost grounds. !!!!!!!!
 
It is usual ratio used to size an accumulator with a solid fuel/ Biomass boiler. Normally the boiler is slightly under sized for the property. With a modulating pellet boiler the ratio/ accumulator can be smaller.
 
Hi desalman,

I agree with ecowarm we also work on the figure of 50 litres of storage per Kw output of the boiler, a modulating pellet boiler will usually over run the requested heat setting, for example a setting of 70c will have the boiler peaking at 77 > 80c as it modulates back because there is a lot of residual heat in the boiler itself and the probes / sensors can't react fast enough.

As well as being a heat store the buffer irons out the peaks and throughs of the boiler output to enable the temperature you ask for to be delivered into the heating circuit, of course there are valves needed to mix the flow and return from both the buffer and the boiler, our preferred system is manufactured by ESBE.

We tend to use pellet boilers that we can control the output from, for example I prefer to be able to have a little reserve that we can call on if needed so in your case I would be opting for a 20Kw output that we can programme back to 15kw as this gives us that little bit of forgiveness for a heating system that may not be performing exactly as specified.

I have found that the heat loss calculations that can be made from various sources such as guides and software are based on ideal conditions, very few (if any) can allow for the different types of radiators, the house on a hill with all four corners exposed to prevailing winds etc so that little extra output can make a big difference.

If we look on our houses are containers that leak heat like a bucket with a hole in it and take your figure of 17kw (rounded up) and convert it to the theoretical bucket with a 17mm hole that we filled from a barrel (warm day) and put a hose 17mm diameter to keep it topped up the water is constantly running just to keep the bucket topped up, for some reason the hole expands to 20mm (extreme cold weather) but our filler hose is still 17mm the bucket starts to empty (temperature drop in the house) so the reserve of 3Kw / mm can be needed.

The benfit of the modulating boiler is we can over size a little especially in old houses without it costing us in fuel being wasted from the boiler constantly cycling, a pellet boiler can use up to 5Kg of fuel every time it starts up however a boiler with a maximim output 22Kw can modulate back to as low as 7Kw, in fuel terms that translates to using 4.5Kg per hour at max output down to 1.4Kg at minimum output.

In my view a succesful installation is one where the average ouput of the boiler is 75 > 80% of the maximum it can deliver as that means we have the boiler using the features that cost the money and the customer has a warm home.
 
So, it looks like an ATMOS 20kw boiler with a 1000 L heat store + all the bits (Laddomat etc ). I suspect Kolty might be getting an enquiry.
 
So, it looks like an ATMOS 20kw boiler with a 1000 L heat store + all the bits (Laddomat etc ). I suspect Kolty might be getting an enquiry.
Easy people to deal with :) and no problem with emails in english
 
So, it looks like an ATMOS 20kw boiler with a 1000 L heat store + all the bits (Laddomat etc ). I suspect Kolty might be getting an enquiry.
With biomass boilers you calculate heat loss and ventilation losses. Lets say this is = to 20kw as in your case.
You then add on the following....
10% for manufacturer efficiency
10% for being with a cold garage
10% for radiator/underfloor heat up

So thats 20kw + 30% = 26kw!

Which is in line with CIBSE, Bre, Snipef, Fidhe and HHIC guidelines.
 
Last edited by a moderator:
With biomass boilers you calculate heat loss and ventilation losses. Lets say this is = to 20kw as in your case.
You then add on the following....
10% for manufacturer efficiency
10% for being with a cold garage
10% for radiator/underfloor heat up

So thats 20kw + 30% = 26kw!

Which is in line with CIBSE, Bre, Snipef, Fidhe and HHIC guidelines.

Heat loss including DHW is estimated at a bit less than 17 kw.

No cold garage involved, boiler will be fitted in boiler room in main house between utility room and kitchen.

Rads have been calculated as a bit oversize using appropriate coefficients.

No allowance made for point source log burner in sitting room which will 'offload' the sitting room heat requirement when its lit during winter evenings.

I suspect the idea of a 20Kw boiler is a best bet, better than my 15Kw comment. The cost difference is not that much. A 1000 l accumulator matches the 1:50 ratio quoted and is an easier option than my original 2000 l unit, and considerably cheaper.

I anticipate using a 200 l DHW unvented cylinder fed from the CH system to the heating coil. There are only two of us and our DHW requirement is not mega as we only have showers not baths.
 
Status
Not open for further replies.

Reply to Thermal Store/Accumulator in an s-plan system in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have just had a boiler, hot water tank and power shower pump replaced on advice by my plumber. I have two separate boilers, heat/hotwater...
Replies
3
Views
438
How a thermal store boiler works! I’ve got an old thermal store boiler and I’m trying to work out how it works. From what I understand the boiler...
Replies
3
Views
511
Background 24 apartments are equipped with thermal stores of (100 to 150 litres) with immersion heater capability. Individual demand of each...
Replies
4
Views
306
Hi all, I wanted to ask a general question about an underfloor heating system our plumber is proposing and if this solution will be sufficient...
Replies
1
Views
467
P
I am having a new system boiler to replace very old cast iron open vented jobbie. heating engineer has offered an S plan system and a Main eco...
Replies
0
Views
268
Podengo
P
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock