S

stevo23777

Hi Guys

I currently have a combi boiler with a single prog stat wired direct to the boiler. I am putting in UFH in my kicthen diner and have to zone off using an S Plan Plus config. I have a Worcester Bosch boiler. I have drawn up the attached wiring diagram, would anyone be able to verify if I have made any drastic mistakes (I don't have a HW cylinder).

Many Thanks
 

Attachments

  • wiring diagram.pdf
    9.8 KB · Views: 53
Doesn't look quite right - the boiler switched live should come off the orange wires from the 2-port valves to prevent boiler firing until valves are open.

Also switched neutral (Ns) is redundant.

Why don't you just download the S+ plan wiring diagram from the Honeywell website instead of reinventing the wheel?
 
Apologies the grey wires in my diagram should be orange, which go from 'activated' zone valve to live return on boiler. The Ns according to boiler manual is Neutral Supply not switched neutral.
Wanted to draw up my own diagram as the timer and stat are single 'appliances' and I don't have a cylinder so it confuses me less!! Also - another question if I can, the UFH has a manifold mixing pump, should this be activated from block 10 also so it only kicks in when boiler is activated? Although in this diagram it will start if either CH or UFH are activated, so should it be run from block 5 switched live?
 
Take it you're gsr? You can't be opening up your boiler if you're not.

Depending on which model it is of course.
 
Apologies the grey wires in my diagram should be orange, which go from 'activated' zone valve to live return on boiler. The Ns according to boiler manual is Neutral Supply not switched neutral.
Wanted to draw up my own diagram as the timer and stat are single 'appliances' and I don't have a cylinder so it confuses me less!! Also - another question if I can, the UFH has a manifold mixing pump, should this be activated from block 10 also so it only kicks in when boiler is activated? Although in this diagram it will start if either CH or UFH are activated, so should it be run from block 5 switched live?

Yes, then it's OK. As already confirmed, terminal 5 for the UFH pump. I still don't like the layout though. Why don't you put L, N, E into the wiring centre then everything including the boiler connects into that rather using the boiler as a junction box?
 
Status
Not open for further replies.

Reply to S Plan Plus - Wiring Diagram in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
170
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
265
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
504
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock