Hi Everyone
I am relatively new to oil, have done my exams and registered with OFTEC but am lacking general experience. I have a boiler issue and wondered if someone could help.
The boiler is a Worcester danesmoor 18/25 fitted with a Riello RDB2.2 and supplied via a Tiger Loop. The boiler is just over a year old and was occaisionaly cutting out some times once or twice in a couple of weeks and then would run fine again. Recently it has been getting more frequent.
I looked at the boiler yesterday, changed the oil filter. connected up my presure gauge and plugged in the FGA.
The oil pressure was a little bit low (105psi) and the needle on the gauge was jumping around a fair bit. I have tried to increase the pressure but the needle on the guage keeps on jumping around. It also took quite a bit of turning to bring it up to 125psi. Does this indicate a faulty pump or another problem? On other boilers I have worked on the pressure guage normally stays quite stable.
Many thanks in advance for any help.
Regards.
 
Hi Quattro,

From my experiences that could be caused by several things, although assuming a faulty pump is the logical thing to do, you should also check out the pump drive coupling to see if it is worn and perhaps the pump is slipping. Are there any other filters in the oil supply line? Have you checked the pump filter itself? Have you checked all the oil connections to ensure they are secure and not allowing air to be sucked into the line. You should also confirm that you have good fuel flow to the pump, and that there's no blockages/partial or other wise? I'm not experienced enough with Tiger loops to advise there, there will be other forum members who can I'm sure. It could be the pump, but........................
 
When the boiler is running check and see if there are any air bubbles going into the tigerloop, air would cause the fluctuation, it could also be the pressure adjustment which is faulty which would also account for the lack of fine adjustment. If air is showing in tigerloop you will need to check the integrity of the joints on the suction side.
 
As above, probably pump but check supply including flex - is this twisted? What sort of filter is it - if its those awful tank ones with the red cap on the sight guage, it could be the metal strainer underneath being blocked up.
 
Also check that your valves are open and that there are no blockages in the tank. Check the tank vent too.

Had something similar a while ago, kids had mostly turned the valve off at the tank.
 
Thanks for all your replies, it turned out there was another filter 1/2 way on the supply line right a the back of the house obscured by a shrub!! the current boiler was installed in a different position and the original line extended and run underground round the side of the building. When it was done the old filter was left on and was filthy. Now thats been sorted the boilers running fine.
Cheers.
 
Status
Not open for further replies.

Reply to Riello RDB 2.2 oil pressure fluctuating. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

C
Hi all, all new to this breakdown life, currently waiting on getting on a training course, so just been relying on technical and instructions since I passed my oftec. The current boiler is a two pipe line off a tiger loop. I went to a Grant vortex boiler last week where the boiler went into...
Replies
0
Views
1K
CJAY40
C
Hello alll, I have a firebird combi oil burner with the riello burner rdb in. It was working perfect up untill yesterday where it's going straight into instant lockout and won't do anything. Not fuel related because I can see it squiring out. Any guesses to what it could be ? Thank you
Replies
7
Views
2K
My Grant combi oil boiler is giving me quite a headache at the moment. When I returned home last Friday I'd no heating or hot water. An engineer called the next day and diagnosed a faulty pressure switch. This was changed and everything seemed ok. However then the boiler began to lose pressure...
Replies
3
Views
555
Hi All, We have finally decided after a bit of a persuasion to have installed a utility room in our garage that currently houses our oil boiler. Initially we thought the boiler may stay in place but after discussions with the builder we would have to move the boiler to replace the floor and...
Replies
7
Views
847
P
Combi boiler system losing pressure every 2 days. We've been topping it up for months now and have had various radiators replaced and flooring pulled up downstairs around each of the radiators but so far no leaks have been found. I'm at a bit of a loss of where the leak can be because given...
Replies
2
Views
1K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock