I have a Glow Worm Ultimate 50FF that has pump over run after the timer switches off. It is a sealed megaflow system. It strted a couple of weeks ago.
There is a brand new single fused pcb in it. All the stats are working and call correctly and valves open & close correctly. Everything else appears to be OK!!
Even if I remove the timing control panel, the pump still runs on.

Does anyone have any thoughts please.

(Can a sticking microswitch in an actuator valve cause this problem??)

Thanks in advance.
 
you need to find out if the pump is wired directly to the boiler or via motorised valves, if direct to the boiler the pcb is faulty if via a motorised valve chances are the valve needs replacing
 
Status
Not open for further replies.

Reply to Pump overrun On Glow worm Ultimate 50FF in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock