I agree with your assessment that it's at the burner but as it's clearly causing me a problem I'm open to all suggestions as food for thought while I'm lying on my sunbed by the pool
I did check that there was a good flame at the burner so it might be the transformer, or the leads, but surely that would cause an intermittent fault with the initial firing as well. It fires every time, after the reset but still goes to lockout

Once the flame is ignited (even just to make my point, if it were to be ignited by a match!) the burner should continue to operate.
Shutting off a few seconds after flame is established suggests control box, but can still be photocell faulty.
Transformer wouldn't have anything to do with lockout once it starts the flame.
Got to check the oil pump to motor drive shaft and drives are not worn and slipping.
Only you said the oil pump is renewed, I would also say check oil pump hasn't a broken drive pin
 
I miss read the problem, I thought the burner ran for 9 sec and went to lock out due to ignition failure
 
Sterling 50 manual in pdf
 

Attachments

  • Sterling Oil Burner ST 50-2 UK.pdf
    412.2 KB · Views: 5
Check for loose connection in control box base. Also check if it's over aired.
 
You could run it on an alternative supply of fuel to eliminate any problems with the tank, fuel line, check valve etc, but like best says, not going to divulge exactly how I would do that on an open forum.
 
Status
Not open for further replies.

Reply to Problem getting burner to keep firing in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I'm looking for some advice on a frustrating problem I'm having with my old Eurostar 50-60s oil boiler please? Although it's old, most parts...
Replies
3
Views
767
I have a customers trianco burner that starts from cold ok for a few minutes (say 3minutes) then locks out then will not stay on. Boiler had not...
Replies
1
Views
634
got new oil and tried to start my reillo g3b oil burner ,when it idnt fire and went to lockout i bleed the pump and check the nozzle ,and...
Replies
6
Views
695
  • Question
Hi. I have a viesmanm vitodens 50 but I've noticed it's behavior change recently I think. When running a bath for example, the boiler will fire up...
Replies
3
Views
1K
Hi, Can I pick your brains? My boiler is often reluctant to start, sometimes it does, sometimes it seems that it will if the demand is from the...
Replies
19
Views
1K