293
Hi
Has anyone come across this small bore copper pipe that runs off the central heating. The pipe runs up to the roof space and terminates in the central heating small feed tank. It seems to act as a vent or overflow for whenever the client turns on the hot water. The coil heats the water and as it heats up, it causes water to go up the pipe and start to fill up the central heating feed tank. This causes a problem because it causes the feed tank to overflow on a regular basis.

Any thoughts would be useful

Thanks

Paul
 

Attachments

  • 20200708_191620 (1).jpg
    20200708_191620 (1).jpg
    92.1 KB · Views: 15
  • 20200708_191620.jpg
    20200708_191620.jpg
    92.1 KB · Views: 16
1. The boiler should (unless it is a system or combi boiler) have a 22 mm vent pipe running from the boiler to an inverted "J" of pipe with its open end above the F&E tank.
2. If that pipe is being used as the vent pipe then:
2a. It is too small in diameter.
2b. Goes through a valve which could close off the direct route from boiler to F&E
2c. It is dangerous with respect to either problem.
3. It may be that vent pipe is a different pipe, not shown in your photograph. In this case the 15 mm pipe is being used as the feed into the boiler's primary circuit. If this is the case:
3a. It still shouldn't be pushing water into the F&E tank.
3b. If it is, then there may be an issue with the pump being set to too high a speed, or some other pipework problem causing the issue.
4. You need to trace and publish photographs of the runs of pipework between F&E and the boiler's primary circuit for a more definitive answer.
 
Looks like that 10mm pipe is what passes for an open vent.
The pipe running along side is probably the cold feed.
Not surprised it pumps over! Needs urgent attention
Get plumber to it a.s.a.p
 

Reply to Overflow pipe off heating system in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
174
PSxxxxxx
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
337
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
189
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock