As above new boiler fitted and new Hive, Hive is set up correctly and works as it should but when it comes to scheduling on/off times via Hive the boiler doesn't cooperate, the radiators are set at 50 on the boiler but when the temp drops below this on the boiler it fires up. Now my way of thinking is I don't want the heating on during the day but the boiler thinks I do. Any help would be great, I have done the switch off and on with the boiler and the Hive.
 
The 50 on the boiler is the flow temperature. It should be at around 70.

It does sound like a wiring issue. Can you take the rubber caps off the lower panel out and unscrew it, you'll see a wiring panel with an electric symbol, if you unscrew that and then take a photo of the wiring it will be easy to tell if they've left the link in or wired the hive into the wrong spot.
 
It won’t make the rads undersized and delta T for rads shouldn’t be affected. If anything it’ll help with the condensing side of things.
Delta T = (flow + return)/2-room temp

At 50 flow you're Delta T is going to be 30 at a maximum using 20 as a room temperature. That would require some massive radiators. For example a 600x1200 p+ at a Delta T of 50 would require a 600x2400 p+ for a Delta T of 30
 

Reply to New boiler fitted Alpha E-Tec 28. in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

J
  • Question
Hi - this is driving me nuts and I can’t figure it out so any thoughts welcome. The hive receiver at the boiler is correctly receiving a signal...
Replies
3
Views
7K
Deleted member 120897
D
    • Like
Hello, my Mothers heating failed in the recent UK cold snap. I found the pump was stuck. I have a question about pump orientation. The...
Replies
8
Views
669
New Boiler - Viesmann Vitedans 100-W 35kw Boiler Problem - Central Heating not working Central Heating is controlled by HIVE. Boiler was...
Replies
11
Views
2K
  • Question
Have a sytem boiler with unvented cylinder with 2 heating zones plus hot water in a house we moved into recently. To start with we were always...
Replies
8
Views
444
  • Question
Hello all, I’m looking for some advice on my Vaillant boiler, which is controlled by my Hive thermostat. I have set the radiator flow temperature...
Replies
1
Views
2K

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock