johnnypiano

Hello;


I have a Gledhill Boilermate 2000 and a Micron 60ff boiler. The Boilermate has 2 unrepairable leaks and i need to replace the system.


Is a Megaflo system a suitable alternative? a few plumbers have mentioned that system and just want to check it will do all that the boilermate does and is a reasonably simple replace/install. ( for a plumber! )

Will i still have instant hot water. The mains pressure is suitable, there is space for an overflow pipe!

I am a total novice! , the Boilermate is on the top floor, the boiler is in the garage.


Thanks in advance for your help.


John
 
Based on cost I'd probably go for a santon premier plus.

But yes it is suitable. Done many, the tricky bit is getting the discharge to outside and getting a decent fixing to plasterboard walls for the expansion vessel
 
depending on your incoming mains pressure you may loose some presure as unvented is restricted to 3 bar which is more than enough
 
Status
Not open for further replies.

Reply to Megaflo to replace boilermate 2000 with Micron 60ff Boiler? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
My daughter's place has a small water leak on a ground floor radiator valve. The radiator pipework is small diameter.i.e 8 or 10 mm. A plumber is coming back in a day or so to make necessary repairs. I am a little concerned as the house has a Boilermate 2000 on the upper floor and the...
Replies
3
Views
351
I recently moved into a flat with a Gledhill Boilermate 2000 and a Glowworm Micron boiler. I have no idea how to use this properly/efficiently and I don't want to end up paying through the roof on gas! The manual is quite confusing but states that the boiler should be kept on max temp at all...
Replies
1
Views
2K
I am looking to replace my existing Vaillant heat-only boiler with a new Vaillant ecotec plus 630 system boiler (30kW). I have a megaflo hot-water cylinder, a central heating system (serving 21 radiators) and an orangery built last year (6m x 4m) with underfloor heating. Through running some...
Replies
2
Views
504
Hi, I am replacing our 11 year old boiler (due to H.Ex. leak) with a new one. This is in a "sealed" system with red expansion vessel in airig cupboard & a megaflo (no tank in loft). However the exisiting boiler is Vaillant ecoTEC 4xx boiler - which is satated by vaillant as an "open vent" boiler...
Replies
3
Views
454
I'm renovating my house which has a standard Vaillant boiler and tank in the cellar, and a tank in the loft. The house will have 2 bathrooms, and is a largish Victorian house (3 floor, but bathrooms are on half landings, at 1.5 and 2.5). Will have UFH on ground floor I've had the lead main...
Replies
2
Views
2K