L

Laurie49

Hi, I've got a Potterton Promax He Store boiler and one of the valves is leaking on the filling loop when it's closed. Doesn't leak when it's open. Other valve isn't leaking externally but must have a slight problem in the valve it's self as the pressure is constantly rising.. Is there any way I can quick fix this so I can go to bed?
Cheers
 
Fill kettle so you can make a brew, fill bath so you can flush the loo.
Turn off mains water, stops pressure rising and keeps heating going.
Fit new filling loop in morning.
 
If unsure about replacing filling loop, purchase two brass caps 1/2"BSP and two 1/2" rubber shower washers. Flexible part of filling loop can then be removed and connections blanked using caps with washers inside to make seal. Restore mains water for hot and cold plus heating.
Brass cap ref: Toolstation code 39862
 
The flexi pipe should always be disconnected and never left permanently attached. It is only meant to be used to fill/top up the pressure and then removed and best practise as joni os pointed out is to cap the valves off once flexi pipe is removed.
 
Status
Not open for further replies.

Reply to Leaking filling loop in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

If you are qualified to do a Gas Safety check on a property I assume that entails checking the boiler. If, when checking a Combi, you notice the...
Replies
9
Views
321
Hi Folks, Where is the place to order a Vaillant filling loop, please? I looked around on the net but can't seem to find it as a kit. I'm not...
Replies
3
Views
147
On my Valliant eco tec boiler the pressure guage is on red when cold . I drain a radiator to correct to pressure and it works fine and stays in...
Replies
5
Views
551
Oliver1234
O
In our sealed Megalo system, when hot water tap is used (say in bathroom shower) the megaflo is taking in some fresh water, I guess to compensate...
Replies
4
Views
391
Hi all Moved to flat recently, and the heating is not very good. I realized the pressure is too low, below 1 bar. It is Meibes, product number...
Replies
2
Views
824
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock