Discuss ideal vogue 32 analyser readings in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

mutley racers

Esteemed
Plumber
Gas Engineer
Subscribed
Messages
5,172
I have just installed this boiler. Nice fancy user interface. In service mode in max rate I am getting

O2 4.2
co2 9.5
Co ppm 129
Ratio .0013

Ratio and co is quite high. Usually when commissioning a new boiler I get a ratio of around .0007 and about 70 ppm co.

Pipe sizing is all fine and that. Flue is all good too
 
Doesn't give any combustion readings in their MI'S when commissioning. Only gas rate and inlet pressure. Does on servicing though. Just the norm, if it's less than .004 great
 
Ideals MI, s are very vague when it comes to commissioning. That's only downside to there boilers. They say ad long as ratio below 0.004 and CO below 200.
 
If inlet, WP and gas rate is spot on, and there are no specifics on CO2, as long as your below 0.004 and 200ppm, then your ok.

I think the Logics run at about 0.0011-0.0014 as well, if I remember right.
 
The co could be burning off the newness inside. co2/o2 slightly gas rich but if ratio's below mi sorted.
 
All the ideals I've fitted although are great boilers they've ALL been set to burn at the same levels.. TBH they could be set a bit cleaner but we abide by Mi's and they're left because they're within limits.
 
I fitted a 26 combi today. It gave a 0.0013 ratio in max mode.
Its within manufacturers spec and was working very well
 
Status
Not open for further replies.

Reply to ideal vogue 32 analyser readings in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Replies
1
Views
173
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
183
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the...
Replies
5
Views
307
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
531
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about...
Replies
7
Views
240
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock