mutley racers

Esteemed
Plumber
Gas Engineer
Subscribed
Messages
5,167
I have just installed this boiler. Nice fancy user interface. In service mode in max rate I am getting

O2 4.2
co2 9.5
Co ppm 129
Ratio .0013

Ratio and co is quite high. Usually when commissioning a new boiler I get a ratio of around .0007 and about 70 ppm co.

Pipe sizing is all fine and that. Flue is all good too
 
Doesn't give any combustion readings in their MI'S when commissioning. Only gas rate and inlet pressure. Does on servicing though. Just the norm, if it's less than .004 great
 
Ideals MI, s are very vague when it comes to commissioning. That's only downside to there boilers. They say ad long as ratio below 0.004 and CO below 200.
 
If inlet, WP and gas rate is spot on, and there are no specifics on CO2, as long as your below 0.004 and 200ppm, then your ok.

I think the Logics run at about 0.0011-0.0014 as well, if I remember right.
 
The co could be burning off the newness inside. co2/o2 slightly gas rich but if ratio's below mi sorted.
 
All the ideals I've fitted although are great boilers they've ALL been set to burn at the same levels.. TBH they could be set a bit cleaner but we abide by Mi's and they're left because they're within limits.
 
I fitted a 26 combi today. It gave a 0.0013 ratio in max mode.
Its within manufacturers spec and was working very well
 
Status
Not open for further replies.

Reply to ideal vogue 32 analyser readings in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
216
  • Sticky
Morning to any Australians lurking around! Register its free, then message me, I'll sort your account out for you. We will need a moderator from each main country too. I'll post this in the Australian forum now.
Replies
0
Views
65
IS IT POSSIBLE TO ADJUST THIS MIXER UNIT? WE HAVE TO HAVE IT TURNED ALMOST FULLY ANTI CLOCKWISE TO GET HOT WATEROUT. THE FRONT PLATE WITH MIRA ON IT PRISES OFF AND INSIDE THERE ARE SOME PLASTIC BITS AND A SMALL CROSS-HEAD SCREW IN THE MIDDLE. THANKS
Replies
6
Views
214
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock