Tony H

hot water tank water too hot, i have replaced the thermostat and element but still the same issue. Th element is housed in a 4" section of pipe fed from the base of the tank to to top of the tank.
Any help appreciated.
Any advice welcome, Tony H
 
I think what you have is a "Willis" heater.
There are pages of discussion about it on this forum:

One of the comments I saw in that thread is about them overheating if the pipes are not sized correctly.
It seems a scheme popular in Ireland, but rarely anywhere else!

Could you just turn the thermostat set temperature down?

FD00186C-7496-4CD2-8792-07066E3F14F8.png
 
Your best bet is to install a pipestat on the heater outlet pipe and wire that in series with its own stat.
I advised that to someone who had increased all the pipework to 22MM and it seems to be working pretty well.
 
Last edited:
Meant to post this trend last year Tony, but better late than never.
Not mine, but this is used with solar pv to divert the output to a 3kw element on a vented 120L HW cylinder,
a pipestst is used to switch the element on/off and the immersion stat(s) are used in a supervisory role as the control stat ( a few tried) just couldnt/wouldnt give consistent switching, it would seem that these external immersions will only run at very high outlet temps even though I've never seen any complaints from the thousands of users.

The green line is the Ipower (export) switching in/out as the pipestat cuts in/out, the power is the scaleX10 (watts) Blue is the temperature at the cylinder bottom.
Yellow is the temperature at the cylinder middle.
Red is the temperature taken on the 22mm pipe from the immersion top.

Would also suggest installing a 2kw element if available as you can see that the outlet temperature falls by over 10C as the power output approaches 2kw or lower.
 

Attachments

  • Willis Temps and IPower.png
    Willis Temps and IPower.png
    263.9 KB · Views: 7
Last edited:

Reply to Hot water too hot, changed element and thermostat in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I...
Replies
8
Views
355
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
182
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer...
Replies
4
Views
276
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
402
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m...
Replies
6
Views
288
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock