3
Hi i hope someone can help, a couple weeks ago boiler was not staying on so i thought i would check rads and i bled them and it fired up and was working for a couple of weeks. Now it fires up and cuts out after about 5 mins. I changed the 2 port valve as pretty much every year this fails. Still doing the same, ive checked the pump and it seems to be turning. Any ideas?? Really could do with some help.
 
Pump sounds like overheating
 
The boiler cuts out...not sure if the burner locks out :(
If the burner was locking out you would have to press the manual reset button on the control box every time to initiate a start/run sequence. You haven’t mentioned you doing that therefore the problem isn’t the burner. Could be on the controls elsewhere on the system or the pump as mentioned above.
 
If the pump is struggling or failed altogether your boiler primary flow will feel very hot and I’d expect a large ΔT across the boiler.
Of course it might not be the pump. Perhaps there’s a problem on the controls side like I said, or maybe even a loose neutral somewhere.
 

Reply to Grant Euroflame Oil boiler in the Oil and Solid Fuel Forum area at PlumbersForums.net

Similar plumbing topics

Hi all, I have a wallstar combi oil fired boiler. We got low on oil a couple of weeks ago but didn't run out. Since we've had our oil delivered...
Replies
6
Views
665
Z
  • Question
My oil fired boiler won’t fire up it is in lockout After a power cut my oil feeder is showing out of fuel- it isn’t. And now my boiler is in...
Replies
1
Views
592
G
I have a danesmore 20/25 oil boiler and it is firing up but it’s producing no heat to the water or the radiators My next door neighbour an...
Replies
1
Views
425
Hi Oil experts. I had a grant wall boiler with a failed transformer. Carried out a service and pretty sooty nozzle, and baffles build up suggest...
Replies
5
Views
278
Any advice welcome as plumber stumped Had 36-46 grant vortex utility boiler 7 years no problem recently oil tank move and tigerloop install...
Replies
4
Views
620
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock