Discuss Grant Euroflame Oil boiler in the Oil and Solid Fuel Forum area at PlumbersForums.net

Messages
3
Hi i hope someone can help, a couple weeks ago boiler was not staying on so i thought i would check rads and i bled them and it fired up and was working for a couple of weeks. Now it fires up and cuts out after about 5 mins. I changed the 2 port valve as pretty much every year this fails. Still doing the same, ive checked the pump and it seems to be turning. Any ideas?? Really could do with some help.
 
Pump sounds like overheating
 
The boiler cuts out...not sure if the burner locks out :(
If the burner was locking out you would have to press the manual reset button on the control box every time to initiate a start/run sequence. You haven’t mentioned you doing that therefore the problem isn’t the burner. Could be on the controls elsewhere on the system or the pump as mentioned above.
 
If the pump is struggling or failed altogether your boiler primary flow will feel very hot and I’d expect a large ΔT across the boiler.
Of course it might not be the pump. Perhaps there’s a problem on the controls side like I said, or maybe even a loose neutral somewhere.
 

Reply to Grant Euroflame Oil boiler in the Oil and Solid Fuel Forum area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
205
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
158
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
278
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock