Hi All

I have a Ferroli 701 Optima which leaks water through its CH 3 bar safety pressure relief valve. The water pressure on gauge NEVER goes above 1.2 bar though (with CH on or off). When i do put pressure in the PRV passes and it drop to zero over 10mins.

The Pressure Gauge USED to go over 3 bar a few weeks ago but is as above now?

There are NO leaks on the system.

I have had the filling loop on constantly to keep pressure on, boiler to work.

I then replaced the PRV and it's still the same...(i also tested the old one as it was working fine)

I am now thinking it may be the expansion vessel (i presumed it never had one as it's states optional on the PDF and shows to the side of the boiler/rectangular) BUT i have since found out it is round and at rear at boiler and i can get access to the schrader valve.

I pressed in the centre bit and NO air or water (thank god) came out, this at at 1.2 bar (which as i stated it NEVER goes above?)

It looks like the XV needs to be at around 1 bar/25 psi, the ONLY pump i have though is a bike higher pressure track/floor pump for my racer (160psi).

What should i do next, i did put the pump on XV whilst it was at 1.2 bar and pressure did increase, giving and good indication that the XV balloon is OK.......?

I am thinking of draining a few litres out of the system and then trying to pump to 1 bar but it will be VERY roughly around that mark due to pump..(i'm not paying £35 for a proper one fro vessels!!)

Any advice much welcome.

Cheers
 
Time to get a gas safe engy in
 
Status
Not open for further replies.

Reply to Ferroli Optima 701 - Pressure Relief Valve passing? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
184
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could...
Replies
0
Views
258
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about...
Replies
7
Views
240
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the...
Replies
5
Views
307
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer...
Replies
4
Views
277
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock