Hi, looking for advise about freezing a pipe on the central heating system. I’m adding a new radiator to the system in another room and thought that a good way would be to freeze the pipe where I need to take off and return to the other pipe. I will be using push fit joints. My question is if I freeze the pipe can I cut it half way in the frozen area or would I have to freeze two different places and cut between them. Hope that you can point me in the right direction. Cheers Paul.
 
If you want to go down the freezing route I would recommend freezing either side of the area you want to cut.

Before starting make sure that any circulation pumps/boilers are not running and allow the system sufficient time to cool to speed up the freezing process as well as reduce any potential scalding risk if exposed to the water/pipework.

Ideally, if there is suitable isolation valves on the system or existing radiators preferably utilise these to isolate legs etc. instead. If you can get away with draining a small section of pipework, it's probably the easier option.

Make sure suitable PPE is worn when it comes to potential contact with any existing inhibitors/biocides in the LTHW system and make sure they are topped back up afterwards to suitable ppm levels if chemical has been dropped or the system total litre size has been expanded through pipework modification.
 
Personally I'd advise draining to carry out the work, fit the new rad run pipework back to where you intend to connect into the system leaving only the connection to do, isolate electrically drain the system place a heavy duty black bag under the pipe to catch any water left in the pipework cut into the pipework fit tees, connect supply pipes refill and flush the system add fresh inhibitor once your confident you have no leakage vent and carry out a heat test . Kop
 

Reply to Cutting on a fropen central heating pipe in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
182
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
220
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
224
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
315
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock