Discuss Cobi boiler fires up when thernostat timer is of in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
S

Ste115

Hello,

I have a new CH system installed with ufh downstairs andradiators upstairs. I have three thermostats, two downstairs and one upstairs.



The issue I am having is that the boiler fires up every15mins or so for around 30 seconds then goes off even when the thermostats areoff.

Any ideas would be most appreciated.

Thanks
 
Have you got the hot water pre heat set to on? What boiler is it? What sort of thermostats are they? What's the setback temp on the thermostats if they are digital?
 
My boiler does not have a hot water pre heat function. The boiler is a Heatline Capriz Plus, the thermostats are Heatmiser Neo and the setback temp is 5 degrees.

Cheers
 
Are you sure the boiler isnt wired up wrong and in fact it is one and running through the boilers internal bypass. Potentially the thermostats may well be linked to zone valves which are shut causing the small circuit and the fact it is only on for a few seconds. Worth checking wiring to boiler and ensuring there is no switch live even when boiler clock / stats are off.
 
what your describing does kinda sound like pre heat function, im not familiar with the boiler but is there a menu function it could be put on or off , otherwise there may be a zone valve stuck open or a problem with the wiring,
Is any pumps on ufh or anything heating up when the boiler fires up ???
 
i take its a system boiler lol no pre heat haha,,,, or is it a combi
 
I had a look at the wiring centre last night and the only thing that saw which I thought was different was the way in which Zone 1 was wired up (circled in red). I have three of the same thermostats highlighted in green and they are all wired up the same.
Below is the wiring centre diagram and below that is a photo of my wiring centre. Due to the fact that I didn’t have a hot water thermostat the plumber wired it up as below.
Wiring centre.jpgmy wiring centre.jpgdesk.jpg
 
Last edited by a moderator:
Status
Not open for further replies.

Reply to Cobi boiler fires up when thernostat timer is of in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Vailant EcoTec Boiler with a Megaflo. These are controlled by a Honeywell controller. I have one 3 port diverter, where one of the...
Replies
5
Views
276
Hi there. I have Grant oil fired boiler which when cold, takes multiple times to fire up. It will run for say 20 or 30 seconds with hot exhaust...
Replies
1
Views
764
Hi all, I have a wallstar combi oil fired boiler. We got low on oil a couple of weeks ago but didn't run out. Since we've had our oil delivered...
Replies
6
Views
655
G
I have a danesmore 20/25 oil boiler and it is firing up but it’s producing no heat to the water or the radiators My next door neighbour an...
Replies
1
Views
416
I am having a problem with my main 24he boiler where the flame is constantly clicking on and off with the heating and when using hot water. Some...
Replies
6
Views
455

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock