I believe i have a very serious blockage in my feeder pipe from the tank to the pump in my central heating system, The pipe work is copper. but probably at least more than thirty years old. I have a magna clean fitted. So the water in the radiators is extremely clean I had both F10 and F1 added to the system. But this has not stopped the bacteria in the pipe . probably because it is front of the pump ... any ideas what the cause and any remedies i can use..
 
Blocked feed is caused by poor system layout. And years of pulling air in. .
It's easily fixed by replacing the blocked pipework and finding the cause of air ingress
 
Have you had the small tank cleaned ? has it got a lid ? its dirt from small tank pipe will need cutting and cleaning will be blocked where feed from tank is connected to system common problem on old tank fed systems
 
On an old system the feed pipe , expansion pipe and pump will be all over the place , all 3 want "close coupling " .
You may need a plumber in , but if you fancy a go google "close coupling " unless somebody else could help with a diagram
 
Status
Not open for further replies.

Reply to Central heating. Blocked feeder pipe from Attic to pump. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi thank you for letting me join this forum . We have an air to water heat pump but the bungalow is piped in micro bore 10mm pipe which doesn’t...
Replies
4
Views
368
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
509
losing pressure
L
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem...
Replies
9
Views
403
Hi guys. A couple of things. 1 am I better fabricating bends in 14 mm copper for my ch or are 90 degree elbows fine, ref flow, friction ect. 2...
Replies
0
Views
312
Hi, Over the past few months, my wife and I have noticed a constant pulsing sound throughout the house which is particularly noisy at night (this...
Replies
4
Views
680
Back
Top