Hello people

Need help git issues with my vailiant ectoec

Was having plastering done removed some radiators this is when the problem started .

The boiler pressure kept dropping and when heating was on pressure would go to high . Had the expansion vessel re-pressuried and pr valve changed . Radiators have been put back on

I am still noticing the pressure the still dropping but lot slower . For example it was 1.6 yesterday this morning gone down to 1.0
any ideas what could be causing this
 
That's a decent amount of water being lost. Try and dry the pressure relief pipe outside as best you can and then monitor it to ensure its not that.

The other obvious checks are visual leaks where stuff has been touched, maybe the drain off. Maybe when they were taking rads off they've loosened a pipe under a floor so check ceilings for damp spots.

The other check is to ensure you're not checking the pressure difference between hot and cold, ensure you only check it when cold
 
That's a decent amount of water being lost. Try and dry the pressure relief pipe outside as best you can and then monitor it to ensure its not that.

The other obvious checks are visual leaks where stuff has been touched, maybe the drain off. Maybe when they were taking rads off they've loosened a pipe under a floor so check ceilings for damp spots.

The other check is to ensure you're not checking the pressure difference between hot and cold, ensure you only check it when cold
No damp spots on the celling. I have put a bag around the pipe outside which will be obvious if it leaks water . Other than that one radiator was taken off downstairs unless there is a leak there . Be a nightmare go find I just had flooring laid
 
Turn boiler off and leave off overnight for this test.

Top pressure up to 1.5 bar cold. Close flow and return valves under boiler. Check pressure in the morning. Is pressure still 1.5?
If yes, no leak boiler side.
Open boiler flow and return valves. Does pressure now drop? If yes, leak is heating side.
Then go looking.
 
No. It is possible the pressure relief is the cause which only leaks when hot as your expansion vessel may not be set right so just because the pressure doesn't change overnight doesn't mean the boiler is ok. It may possibly be a good test though to see if the pressure drops after you open the valves back up to see if the pipework is leaking. Don't forget to turn your boiler off at the switch if the valves are shut not just off the on programmer to save killing your pump if it decides it wants to come on for what ever reason

Check the pressure when cold then check it a day later when cold again and see if you have a drop. Check the pressure relief outside to make sure that's not dripping. Then check as much of the heating system visually throughout the house
 

Reply to Boiler pressure issue in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
126
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
117
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
231
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock