AllyBongo

Plumbers Arms member
Plumber
Gas Engineer
Messages
502
Got a fresh batch of gas certs/services to do for a new landlord, 1st one I go to has a Baxi 105e, tenants shows me that the gas hob goes out when the boiler fires up! Turned out the gas valve handle was off and the valve was just cracked open, this boiler was seemingly serviced by BG in August!!

Anyway, opened the valve and the working pressure was fine, however the boiler was having some issues. On hw the temp was ramping up the burner was cutting out. High bp was 12mb, so a tad low. Got the low bp to 1.8mb. Suspected pex, but when i turned the hw stat down the gas valve did not modulate, even right at the lowest setting. Flow rate wasn't as high as it should be, but not worryingly low. On heating it fired on low burner then slowly ramped up, so I assume the gas valve is ok.

Didn't want to spend much time at it, as with the overall condition of the boiler it could be a replacement job. But will be speaking to the landlord tomorrow to see if he wants it diagnosed and repaired or down the new boiler route. Any common issues with these, I remember another one a while ago that we ended up replacing wouldn't go to low burner with one of the black wires removed from the mod coil, slightly different, but always annoyed me what was causing that too...
 
Blocked plate it sounds like.

These boilers stay at high rate for ages before modulating down, but might be worth checking the resistance of the thermistor
 
Really? Do they always fire on full burner? Even if the hw stat is at its lowest setting?
 
Status
Not open for further replies.

Reply to Baxi 105e in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
531
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
251
PSxxxxxx
P
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
184
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
182
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason...
Replies
3
Views
304
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock