Merry xmas
How clean/ dirty was the water when the pump was taken out?

Hope the consultant can sort it
 
Merry xmas
How clean/ dirty was the water when the pump was taken out?

Hope the consultant can sort it
There was a little rubbish, not much really. Chemical cleaner was being used, then flushed through for quite a while.
 
Like I said before isolate manifolds get flow to cylinder hot, so hot u cat touch , leave hot taps running so that cylinder is full of cool water. Turn on say m1 then wait, once return from m1 ok leve it on and turn on m2 keep going until the flow to cylinder cools so u can hold it.

Temps are relative so just wrap a thermometer in a cloth soaked on veg
Oil on pipe. Just enough cloth to hold bulb against pipe . Oil is just to conduct heat as water will evaporate .
Or buy a flexible plastic ones and stick to pipes , the film types.

Each manifold has it's own pump right? - stupid question but needs to be asked?

I think your plant room needs re configured, 100% LLH with pump set to each circ. cylinder fine , get zone valves fitted on each flow in plant room . Ie to each manifold or cylinder. Shouldn't require any disturbance outside of plant room. I would be fitting an additional boiler or boilers tho . My mind u want at least 70kw for peak demand . Won't say this too loud as not a fan of wb but put same boiler in as what u have or fit multiple new boilers say 2 or 3 ideal logic system 30kw or even two kestons as same boiler but higher output avail.

Don't forget to balance system and lag it properly
 
Like I said before isolate manifolds get flow to cylinder hot, so hot u cat touch , leave hot taps running so that cylinder is full of cool water. Turn on say m1 then wait, once return from m1 ok leve it on and turn on m2 keep going until the flow to cylinder cools so u can hold it.

Temps are relative so just wrap a thermometer in a cloth soaked on veg
Oil on pipe. Just enough cloth to hold bulb against pipe . Oil is just to conduct heat as water will evaporate .
Or buy a flexible plastic ones and stick to pipes , the film types.

Each manifold has it's own pump right? - stupid question but needs to be asked?

I think your plant room needs re configured, 100% LLH with pump set to each circ. cylinder fine , get zone valves fitted on each flow in plant room . Ie to each manifold or cylinder. Shouldn't require any disturbance outside of plant room. I would be fitting an additional boiler or boilers tho . My mind u want at least 70kw for peak demand . Won't say this too loud as not a fan of wb but put same boiler in as what u have or fit multiple new boilers say 2 or 3 ideal logic system 30kw or even two kestons as same boiler but higher output avail.

Don't forget to balance system and lag it properly
each manifold has its own pump at the manifold not in the plant room. Manifold picture earlier in the thread.
 

Attachments

  • image.jpg
    image.jpg
    94.4 KB · Views: 95
each manifold has its own pump at the manifold not in the plant room. Manifold picture earlier in the thread.

Hi, sorry on an iPhone.

Ok so you have zv on each manifold.
Don't like the 4 port blending valves. Difficult to balance. I prefer pump/ manifold return and primary flow. And then a balance-able return. Notice there is no pipe stat to tell the zv when flow is needed. So it's just open when manifold is on? Not much point in it. IMO , should have a pipe stat set on the returns from floor to blending valve and be set so that when flow cools and blending valve opens up for more primary heat and interlocks with boiler or in your case the LLH pump.

Also what is floor construction? Just that there is no conduit on the ufh pipes as they leave the floor? Always try and have 150mm of conduit above floor and 350 is below to protect from mechanical damage.
 
Last edited by a moderator:
Hi Carrera, To get the IR working you can paint the pipe black :)

Scenarios with testing .... I'd want to know what strain was being put on the boiler, so primary F&R's would be where I'd monitor under as many load scenario's as possible up to max load. If your flow temp drops below 60 DegC it'll start to draw heat out of the cylinders hot water. If the flow temp stays cool for a long time then I'd be pointing towards that being the reason why your hot water isn't getting to temp!

If you haven't already, I'd put the hot water on 24/7 or at least an all day setting.... :)
 
Sorry haven't been able to test much at all, as the system is not really working as it was left for the holidays. At the moment just about able to get warm water, boiler going on and off very 2 mins and the heating was working with a light load, but has now started doing the same. Will have to wait for the plumber to come back next week before I can really try anything
 
Give Worcester a call, your boiler is under warranty with them. You may have a fault on the boiler?
 
Give Worcester a call, your boiler is under warranty with them. You may have a fault on the boiler?
For the hot water, basically boiler fires, flow temp rises (set to 70), modulates lower and lower and kicks off when it goes over 70, water circulates for a couple of mins and then when temp hits about 40 boiler fires again, slowly getting to 70, before we go back round the loop. As you can imagine water takes ages to warm up this way, so have been combining thus with the emmersion over the holidays. I will give wb a call on Monday.

does not do this on heat, gets to 70 and stays there, however this morning started doing above with heating, but after a few attempts of me stopping and starting the heat, it appears to be ok.
 
For the hot water, basically boiler fires, flow temp rises (set to 70), modulates lower and lower and kicks off when it goes over 70, water circulates for a couple of mins and then when temp hits about 40 boiler fires again, slowly getting to 70, before we go back round the loop. As you can imagine water takes ages to warm up this way, so have been combining thus with the emmersion over the holidays. I will give wb a call on Monday.

does not do this on heat, gets to 70 and stays there, however this morning started doing above with heating, but after a few attempts of me stopping and starting the heat, it appears to be ok.

Without seeing what's going on it's difficult to give you anything accurate to be honest Carrera! Are you able to get a reading on the return as the flow is heating? If so there should be around 20DegC difference, thereabouts. If there's a rapid rise in temp to 70 before dropping back to 40 then I'd be wanting to know how well the pump was performing and/or is there a potential flow restriction somewhere? If the rise is gradual and there's a maintained 11-22DegC difference between F&R then Circulation is okay IMHO :)
 
Status
Not open for further replies.

Reply to Advice needed. Issues with underfloor heating and hot water system for new build in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock