Both systems rely on the mains pressure to push the water out of the tap. The only difference is that the unvented cylinder acts as source of hot water in the path between the mains input and the tap, so the water does not have to be heated instantaneously.

If you have five litres/min from the mains, you will get five litres/min coming out of the tap irrespective of which system you have.

Pressure and flow rate are not the same thing.

But if you have 50L/min from the mains you will only get a maximum of around 15/16L/min (in Summer, in ideal conditions) from the best combi boilers on the market. The unvented cylinder will give you 50L/min. That is why mains pressure and flow rate must be checked before fitting either of these products. Dynamic pressure thus also tends to be far better on unvented systems compared to combi boiler systems.

With a combi boiler the hot water to the whole house should ideally be supplied in 15mm pipework. This massively limits the flow rate to the taps as well and causes much larger pressure drops through the system than an unvented setup which will be run in 22mm for significant chunks of the pipe run.

I know you don't directly infer it but lets not try and compare combi boilers to unvented cylinders. An unvented cylinder is a far, far superior solution in terms of hot water performance (assuming the mains is good enough to justify fitting one).

Of course it comes with a far, far superior cost too compared to a combi boiler!
 
Last edited:
That ties in with most of what I've read Bob... The downside I'd read was the complicated nature of the system.

I've had a right evening - drained down the system by removing a downstairs rad, then had to mock up a tap to one of the valves as it was leaking, using push fit, a stopcock and a spare piece of pipe.

Then attempted the gate valve on the pump, what a job! Couldn't get it off to start with then found myself removing the pump to get it out. The pump was so heavily gunked it was ridiculous! I then spent over an hour trying to free up the pumps channels whilst trying to make sure I left no sludge to later block my 10mm pipes. Anyway, the lower gate valve compression joint was too close to a collar so I couldn't get to the old olive and had to refit it with the old compression olive/nut (squeeky bum time), not least as it looked like someone else had attempted to remove it and bent the 22mm pipe out of shape - total gamble when refitting. Luckily I'd bought some jointing compound.... The lower seal was perished so obviously replaced that along with the valve, refilled the system and all is good in the world again! One question though, after bleeding the radiators, can I switch back on the hot water or do I need to bleed anywhere else in the system? I started the pump up briefly and it made a gurgle for a minute then started working, I stopped it however to post up here before going any further.

The other joint on the bottom of the cylinder I attacked with the wire brush, still not clean and full of white crusty stuff. I think I've found the leak though, on the 2nd 90, dry joint possibly due perhaps to the hard to reach location. That'll be a plumber job I think....unless I can cut the 22mm pipe 2 inch from the cylinder and mock up some 22mm push fit bends? Is this dooable?

Assuming after testing that the hot water works fine, tomorrow I'll drain it down again and fit the drain tap valve to one of the lower rads.

Can anyone help regards the question on refilling the system before I attempt to use the hot water?
 
Last edited:
If you have an Immersion on the cylinder, then you can just switch that and use while the heating side is drained down.
If not, then you need to refil the heating system before you use the hot water. After refilling the heating system, you need to bleed the pump by undoing the big screw till water escapes then tighten back screw. As for draining the system in future, you can fit one of these. If all downstairs rads are drop downs, then fit one to everyone of the rads.
Angled Radiator Valve & Drain Off 15mm x ½" | Manual Valves | NoLinkingToThis
 
Thanks village. I've got one of those to fit tomorrow, I just wanted to fill the system back up to check the joints I'd attacked first. I had already released that screw and water flowed almost immediately so presume it's good to go. Gonna warm it up and check shortly.

What do you think about the dry joint, is it worth attempting speed fit given the horrible access? My concern is the proximity to the boiler after reading not to use steed fit within 1m of a boiler. Also is there any detriment to undoing the bolt to the cylinder that holds that pipe in... I could do with removing that pipe to clean before sliding any speed fit on
 
Last edited:
20150815_072951.jpg

This is the joint. I assume it's a standard 22mm compression which will probably need a new piece of copper 22mm. I may buy one of those and a couple of 90 speed fits to hit the pipe disappearing into the floor. Can anyone see an issue with this
 
A plumber with a pipe freezer and a tool like a Fein should have that replaced within an hour or two at most. Slice the pipe once frozen on both sides of the coil, drain water out between ice plugs and solder a nice bit of new copper onto a mew cylinder connector to boot. No pipe freezer and add another hour onto that for faffing about draining and filling the system to do the job.
 
What would that cost be roughly croft? I'm eager not spend given we've just moved in and have a million other things to buy. However if you think it's worth getting a plumber in? I'm probably only looking at a couple years use before it's replaced. Cost of 22mm pipe and fittings comes in at ÂŁ15 for me to do
 
Diy, are you saying I'm likely to get the same drop with an unvented?
No, far from it. I was not suggesting that a combi is superior to an unvented but that, if you are having problems supplying two outlets at the same time with a combi, you will probably have the same problem with an unvented. This is because the incoming flow and pressure determines what comes out.

As for ShaunCorbs unasked question why an unvented can do two baths while a combi can't, the brief answer is: because the water is not heated instantaneously.
 
Thanks doitmyself, and yes I agree that the cold water will reduce the more sources request, but as you quite rightly say, the hot water will be less affected when compared to the combi.

I do find myself with a problem however, currently we are using the electric shower in the main bathroom because we haven't another solution. However what we do with the en suite is still entirely open... Go electric or remain on a thermostat regime - with an increased pressure to make it useable. Bearing in mind that we are considering buying solar panels, electric showers all round could be the answer despite their aesthetics.
 
Croft, I'm taking your advice and getting the plumber around for this final leak. The bolt to the cylinder looks like it has an integrated piece of copper which I'd have to replace, this would then need soldering regardless which is beyond me. I'd love to learn how to do these types of joints eventually, properly.
 
Status
Not open for further replies.

Reply to Advice needed - 10mm system conversion? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
283
PSxxxxxx
P
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
221
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
555
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
444

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock