I have recently moved house and trying to understand how my heating systems work, and this is because it seems to be inconsistent. Firstly to explain my setup, I have a normal heating system with a tank in the loft and cylinder in the airing cupboard and Honeywell wall stat. My house also has an extension with underfloor heating in. This has a digital thermostat on the wall.

What I don't understand is why my heating system is inconsistent. When i use the digital thermostat in the extension, sometimes all the radiators come on in the house and at other times it's just the underfloor heating that comes on in the extension. And when I use the original wall stat in the house, sometimes all the radiators come on in the house (albeit minus the extension), and at other times they don't and I only get hot water. Why? Are the two systems in conflict with each other? I have a separate 3 port valve for each system - could it be their positioning? I notice the lever on the 3 port valve for the original house has no resistance when i push it so I think the motor or whole head unit needs replacing. I touched the motor and it was very hot - i thought it was only meant to get warm?

Thanks for any thoughts!
 
I have recently moved house and trying to understand how my heating systems work, and this is because it seems to be inconsistent. Firstly to explain my setup, I have a normal heating system with a tank in the loft and cylinder in the airing cupboard and Honeywell wall stat. My house also has an extension with underfloor heating in. This has a digital thermostat on the wall.

What I don't understand is why my heating system is inconsistent. When i use the digital thermostat in the extension, sometimes all the radiators come on in the house and at other times it's just the underfloor heating that comes on in the extension. And when I use the original wall stat in the house, sometimes all the radiators come on in the house (albeit minus the extension), and at other times they don't and I only get hot water. Why? Are the two systems in conflict with each other? I have a separate 3 port valve for each system - could it be their positioning? I notice the lever on the 3 port valve for the original house has no resistance when i push it so I think the motor or whole head unit needs replacing. I touched the motor and it was very hot - i thought it was only meant to get warm?

Thanks for any thoughts!
Think you need to change to an s plan heating system
 
As the guys have stated pictures of the system are needed here , a system like this would normally be piped as a Honeywell S plan plus system using three 2 port valves one for each circuit and have timed and temperature control for each ?? Kop
 
Thanks for your replies...photos attached. And just noticed it is a 2 port valve for the underfloor system with a pump, and an additional pump in airing cupboard with 3 port valve.
 

Attachments

  • 20200607_104641.jpg
    20200607_104641.jpg
    86.3 KB · Views: 20
  • 20200607_104910.jpg
    20200607_104910.jpg
    52.2 KB · Views: 23
  • 20200607_104851.jpg
    20200607_104851.jpg
    87 KB · Views: 20
  • 20200607_104717.jpg
    20200607_104717.jpg
    60.4 KB · Views: 21
  • 20200607_104809.jpg
    20200607_104809.jpg
    51.6 KB · Views: 21
  • 20200607_104754.jpg
    20200607_104754.jpg
    51.7 KB · Views: 22
  • 20200607_104700.jpg
    20200607_104700.jpg
    66.1 KB · Views: 23
Holey Moley that looks a quality install on the underfloor.

Best bet is to get somebody on site who is familiar with heating systems and their wiring. Set of testers and some time will get you sorted.
 
With a three port valve your either have heating only , hot water only or both , add in a underfloor circuit then the three port heating circuit needs to be open so the primary heating hot water can circulate around the system and back to the boiler to be heated , the issue you having is possibly caused by the heating water short circuiting and creeping up the return into the radiators ect when it should be off or satisfied, needs a engineer who.know his way round a multimeter and probably a modification from a three port to two 2 ports plus your underfloor valve . Kop
 
A two port and a three port (be it diverter or mid position) makes sense now. There's no reason why this layout can't work, providing installed and wired in correctly. As above try to find someone familiar with UFH and competent with heating system wiring.
 

Reply to 2 seperate heating systems - how do they work together? in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
109
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
234
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
224
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
312
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...