Drain & valve off cylinder coil in that way they can still use the immersion or Solar for domestic hot water.
The heating system pressure should stop rising. If so it is the coil & you will have to order a new cylinder.
 
I isolated the F&R at the boiler at 1.5bar and it held .. Once the return was opened the pressure rose immediately and water meter was turning over .

Probably cylinder coil gone then.
Is it a copper unvented cylinder, or stainless steel?
If you are not G3 qualified, just be aware if no isolating valve on mains supply to unvented cylinder, then only install one BEFORE the combination valve. (Between the combination valve and cylinder must not have any valve)
 

Reply to Unvented heating system, unusual boiler fault in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

P
  • Question
Boiler is SIRIUS THREE FS 70 Potterton commercial. Situation: We are small building contractors and my labourers managed to damage the radiator...
Replies
2
Views
144
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
277
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
292
PSxxxxxx
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
465
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock